I have seen the RPZ and dry valves under the first landing of the stairs, then this area is enclosed and heated. Remember your riser is wet and subject to freezing below the clapper of the DPV. Due to the low overhead and access issue's this arrangement would require AHJ approval, if the 1st landing is less than 7'-0" AFF.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "RFI - Bismarck" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, March 13, 2008 7:24 AM
Subject: RE: Dry System Size


Sounds kinda 'elementary'... but any chance of finding a spot in the corner
of the "L" and then splitting the systems up so that each valve covers a
"wing"?  Stair? No - you'd have to have a pretty wide set-up to allow for
the accessibility requirements! Usually in Parking Garages you're going to have a mechanical room or 'something' which constitutes a room / void space where you can place a couple dry valves. Otherwise, if it's out in the open - make sure that they provide a ton of bollards around the risers to provide protection from the possibility of someone crashing their vehicles into the
system... Ouch!

I do have a couple pictures of the dual zone Dry System that was installed @
the Museum of Glass in Tacoma, WA if you want to contact me off-forum.  It
was in a room no bigger than 8' x 10' with (2) walls dedicated to F.P.

RFI Chuck

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, March 12, 2008 6:43 AM
To: [email protected]
Subject: Dry System Size

Does any have a general rule of thumb they use as a coverage maximum size
for a dry system?  I have an underground parking garage in schematics and
I'm just trying to claim some space for dry valves.  Its over 52,000 SF so
I know it's at least two zones.  It's somewhere between 60,000 and 70,000
SF in an L shape.

Anyone ever install a dry valve in a stair?  Where do you typically see
the valves in a parking garage under a hotel?

John Kaminski
Burt Hill
724-431-1388
http://www.burthill.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG.
Version: 7.5.518 / Virus Database: 269.21.7/1324 - Release Date: 3/10/2008
7:27 PM


No virus found in this outgoing message.
Checked by AVG.
Version: 7.5.518 / Virus Database: 269.21.7/1325 - Release Date: 3/11/2008
1:41 PM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to