I agree. I had a situation in a high pile storage warehouse, where they made
a cage with wire mesh (walls and ceilings)for security. The roof sprinklers
were only 2 feet above the wire mesh ceiling. Inside the caged area there
were racks with storage. I told them they had to add heads below the wire
mesh ceiling with water shields, which they agreed to. The problem I had was
deciding how it was to be calculated. The cage was an afterthought after the
sprinkler system was installed. The roof system was designed for 0.6 density
deleting in-rack sprinklers. I told the sprinkler designer to re-calculate
with 0.6 at the roof and add sprinklers below the wire mesh to the calc.,
treating them as in-rack sprinklers. 

My line of thinking was this case could be treated similar to in-rack
sprinklers and not include all the heads below the wire mesh in the design
area. And I felt both levels had to be calculated. Any comments?

Tony    

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight
Sent: October 22, 2007 1:21 PM
To: [email protected]
Subject: RE: Vertical mesh wall

Bobby,
In my opinion, which isn't always as humble as it needs to be, since this is
not LH, the sprinklers will need to maintain their minimum separation and
the sprinklers will need to be spaced treating this as an obstruction to
discharge (i.e. half the distance).  The mesh will allow water through, but
it will also impede proper distribution.  Because of this I believe that the
minimum distance between sprinklers will need to be maintained to prevent
cold soldering and since distribution will be affected, half the distance
will need to be maintained.

Just my opinion if I were the layout guy,

Bob Knight

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby Gillett
Sent: Monday, October 22, 2007 1:03 PM
To: [email protected]
Subject: RE: Vertical mesh wall

This is Class IV comm and we have EC sprinklers (storage room in
Grocery/Shopping store). Wall of mesh keeps people out of a certain area in
the back store room.

Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight
Sent: Monday, October 22, 2007 2:00 PM
To: [email protected]
Subject: RE: Vertical mesh wall

Since this is in the vertical plane wouldn't this fall into the "MESH"
criteria in 8.6.5.2.2 for LH only occupancies?

Bob Knight 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Monday, October 22, 2007 12:47 PM
To: [email protected]
Subject: RE: Vertical mesh wall

This may or may not help, but >70% unobstructed is what we've seen applied
by a reputable independent fire tester/underwriter on similar items.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby Gillett
Sent: Monday, October 22, 2007 2:39 PM
To: [email protected]
Subject: Vertical mesh wall

We have a 2x4 metal stud wall on 16” centers with ½”x½” hardware cloth on it
to deck. Is this considered a wall?  I can’t seem to find the size
limitations to the openings. 

 

Thanks,

 

Bobby Gillett

Project Manager

[EMAIL PROTECTED]

(731)-424-0130

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date: 10/22/2007
10:35 AM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date: 10/22/2007
10:35 AM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date: 10/22/2007
10:35 AM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date: 10/22/2007
10:35 AM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to