Joe,

They did not do a sprinkler layout-- just supplied us with the sprinkler
type, main location (due to structural load), and density/area for different
areas throughout. We still have to lay it out. 
I don't always agree with their classifications, but when it's in stone and
writing, what can you do? All you can do is get all the info possible and if
there is something wrong, try to inform, educate and hope for the best!! 

Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe Hankins
Sent: Monday, October 22, 2007 3:55 PM
To: [email protected]
Subject: Re: Vertical mesh wall

I don't know that it is written anywhere for walls, but if rack shelves 
can be considered open with wire mish shelving more than 70% open, the 
same would go for walls.

I was just responding to your statement that it was a grocery stock room 
and was class IV. If they have specified how they want it done, why are 
you worried about the wall?

Joe

Bobby Gillett wrote:
> Joe,
>
> Thanks for your reply as well.
>
> I was hoping that the 70% was accurate, but could only find it applied in
> 8.6.5.2.2 as stated in an earlier response, which is for light hazard. Is
> there somewhere else that states that this applies to something other than
> LH?
>
> As far as the hazard classifications, this is an pre-engineered set of
> drawings that has us calc'ing two different ways in the same area. The
> design engineer firm wants these areas calc'd .45/2000 and .55 for the
most
> 4 demanding sprinklers. That is our instruction and other than the town,
> they are the AHJ along with the insurance company and they agree w/the
> design engineer for the project. We have no storage info other than how to
> do it and they state in writing this is how they want it done.
>
> Bobby Gillett
> Project Manager
> [EMAIL PROTECTED]
> (731)-424-0130
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Joe Hankins
> Sent: Monday, October 22, 2007 3:33 PM
> To: [email protected]
> Subject: Re: Vertical mesh wall
>
> Bobby,
>
> If the "wall" is  70% open or more, it would not be an obstruction to 
> sprinkler discharge. You would, however, have to extend the higher 
> density beyond the "wall" because in terms of sprinkler operation, it 
> would be absolutely no different than no wall.
>
> As an aside, there isn't a grocery store stock room anywhere in the real 
> world that meets the criteria for a class IV commodity. Commodity 
> classification is done on a pallet load/carton basis, not the overall 
> mix in the room. If there are plastics or other higher hazard 
> combustibles in the room, then it should be protected for that. If there 
> is nothing worse than a class III, then that's your design.   Unless it 
> is filled with products having no more than 15% plastic in each carton 
> or pallet load, it's not class IV.
>
> At some time of day and season of the year, any grocery store stock room 
> is going to have lots of plastic or worse. You're not designing a 
> sprinkler system to work some of the time.
>
> Joe
>
> Bobby Gillett wrote:
>   
>> I guess my replies got lost, try again.
>>
>>  
>>
>> This is Class IV comm and we have EC sprinklers (storage room in
>> Grocery/Shopping store). Wall of mesh keeps people out of a certain areas
>>     
> in
>   
>> the back store room.
>>
>>  
>>
>>  
>>
>> Bobby Gillett
>>
>> Project Manager
>>
>>  <mailto:[EMAIL PROTECTED]>
>> [EMAIL PROTECTED]
>>
>> (731)-424-0130
>>
>>  
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>>   
>>     
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>   

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to