ISO does not require anything be done to a sprinkler system.  They simply have 
a grading system that assesses deficiency points for items not correct and if 
you get too many points system is graded as non-sprinklered. ISO still requires 
internal pipe exam after 5 years and every 5 years after that on dry systems.  
Biggest single item causing sprinkler system to be graded as non-sprinklered is 
lack of documented inspections.  There is a small I believe 2 point charge for 
3/4 inch pipe. There is also a charge of 5 points for missing cap on FDC.

Top Myers
RelMark Group
961 Pottstown Pike
Chester Springs, PA 19425
O - 610-321-2415 X-219, C - 610-952-0965
[EMAIL PROTECTED]

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Friday, October 19, 2007 9:16 AM
To: [email protected]
Subject: RE: 3/4" Steel Pipe on Dry Pipe System

There are great benefits to replacing 3/4" end of branch line piping with 1" 
piping, especially since there are reasons the standard doesn't allow 3/4" 
steel pipe any longer.  

It's easily plugged with minimal amounts of debris and easily ecluded over 
time.  I agree with you Rick, its a good idea and a prudent practice to replace 
older technology with newer.  We know what we know when we know it and if you 
can convince a client to help himself make a good decision based on sound 
advise, the goals of fire and life safety are being met.

NFPA 25 is still a relatively new document and it's predecessors (NFPA 13A and 
14A) didn't prescribe anything - and as such were not adoptable as codes.  

The pre-cursor to NFPA 25 requirements as they relate to internal condition 
inspections and flushing were found in a small green covered pamplet printed by 
the Insurance industry.  I have a copy somewhere but don't recall the name of 
it exactly.  Anyway, the ISO offices used to send notices out to building 
owners with dry systems 50 + years old, requiring the internal condition 
inspection.  That document and  ISO did require the 3/4" ends of branch line to 
be upgraded to 1".

bc



---- Rick Green <[EMAIL PROTECTED]> wrote: 
> Reduce the possibility of future sprinkler pipe obstructions. Increased 
> corrosion growth evident in dry pipe sprinkler systems, especially with 
> smaller diameter pipe.
> 
> Rick E. Green, District Manager
> East Coast Fire Protection, Inc.
> 1113 Cavalier Boulevard
> Chesapeake, Virginia 23323
> 757/485-7486(p), 757/485-8730(fax), 757/328-0131(cell)
> [EMAIL PROTECTED]
> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight
> Sent: Thursday, October 18, 2007 5:01 PM
> To: [email protected]
> Subject: RE: 3/4" Steel Pipe on Dry Pipe System
> 
> Rick,
> There are no NFPA 13 criteria for changing 3/4" pipe in the manner that you
> have described.  What would the benefit be to your customer to change the
> 3/4" to 1"?
> 
> Bob Knight
> 
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Rick Green
> Sent: Thursday, October 18, 2007 2:47 PM
> To: [email protected]
> Subject: 3/4" Steel Pipe on Dry Pipe System
> 
> 
> East Coast recently completed inspection of a dry pipe sprinkler system.
> During trip test unable to trip the dry pipe system because of foreign
> material causing pipe blockage.  Initially pipe blockage was notice in the
> inspectors test pipe.  After a thorough inspection, majority of the pipe
> including mains, branch lines showed signs of foreign material in the pipe.
> 
> We have proposed to owner to flush sprinkler system and also replace ¾"
> branch line pipe.
> 
> Is their a standard reference that requires removal of 3/4" sprinkler pipe
> with larger diameter pipe (1") when the sprinkler pipe is flushed?
> 
> 
> Rick E. Green, District Manager
> East Coast Fire Protection, Inc.
> 1113 Cavalier Boulevard
> Chesapeake, Virginia 23323
> 757/485-7486(p), 757/485-8730(fax), 757/328-0131(cell)
> [EMAIL PROTECTED]<mailto:[EMAIL PROTECTED]>
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> 
> No virus found in this incoming message.
> Checked by AVG Free Edition.
> Version: 7.5.488 / Virus Database: 269.15.0/1077 - Release Date: 10/18/2007
> 9:54 AM
> 
> 
> No virus found in this outgoing message.
> Checked by AVG Free Edition.
> Version: 7.5.488 / Virus Database: 269.15.0/1077 - Release Date: 10/18/2007
> 9:54 AM
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to