Slow down IMHO. Read the text, don't read into it. If they wanted you to
take the venting and egress exceptions for ESFR they would have said it.
Remember you are also dealing with exception to the base rule. I only
believe you get one in your case. Either skip the vents but add doors or
skip the doors and add vents. Choose the lesser of the evils. Joe will
have a cow, but you could do ESFR and vents and not do the doors. Now get
an FPE involved to PBD the vents and doors with ESFR to balance not full
compliance with either.
Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
763-658-4483
763-658-4921 fax
Email: [EMAIL PROTECTED]
Mail: P.O. Box 69
Waverly, MN 55390
Location: 4439 Hwy 12 SW
Waverly, MN 55390
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Tuesday, October 30, 2007 12:54 PM
To: [email protected]
Subject: RE: 2006 IFC - Smoke and Heat Vents
Thanks Scot. I think the same but I had a local Architect tell me it was
taking the ESFR trade off twice.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of å... ....
Sent: Tuesday, October 30, 2007 10:46 AM
To: [email protected]
Subject: 2006 IFC - Smoke and Heat Vents
my opinion is yes.
scot deal
excelsior fire
On 10/30/07, Fletcher, Ron <[EMAIL PROTECTED]> wrote:
>
> In a high piled storage building may the 400 ft. egress dimension be
> used "without" vents if the building is equipped with ESFR sprinklers?
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)