I have been involved with this situation once. The engineer of record designed sidewall sprinklers 7'-0" A.F.F. 10'-0" max. spacing along the perimeter connected to a deluge system with detectors mounted at the domed portion on the outside of the dome. Don't remember what kind of detector he used to accomplish this. A wet pipe system was used at the roof deck throughout the area above the planetarium. All steel construction.
Ron -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of << 0 o 0 >> Sent: Tuesday, January 08, 2008 8:18 AM To: [email protected] Subject: RE: Planetarium ceilings Many moons ago I did one for Denison University, the EOR wanted vertical sidewalls around the perimeter of the dome. No heads in the planetarium ceiling. Not sure if that came from the manufacture of the dome, GC, EOR or the University. I don't remmber for sure but we may have had heads above the dome too. Bryan A. Dann Dannba Design Services, LLC Fire Sprinkler Designs Office: (740) 363-5878 Cell: (740) 803-0967 [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Allan Seidel Sent: Monday, January 07, 2008 10:53 PM To: [email protected] Subject: Planetarium ceilings If I may tap into the sprinklerforum's years of experience, what is the typical practice for a planetarium ceiling? The planetarium in question has a domed metal ceiling of about 25 feet in diameter. The ceiling material is essentially the same as that of a 12 x 24 metal pan ceiling with tiny holes, except that the pans are curved pie sections. The projector sits at the center and therefore projects normal to the dome's inner surface. It seems to me that three small diameter Viking flat concealed sprinklers would probably have a negligible, if noticeable at all, impact on the projected image. I doubt there would be any shadow because the image arrives normal to the surface. Has anyone done one of these? Thanks, Allan Seidel St. Louis, MO _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) Internal Virus Database is out-of-date. Checked by AVG Free Edition. Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007 1:39 PM Internal Virus Database is out-of-date. Checked by AVG Free Edition. Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007 1:39 PM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)