Why inject practical reality into the discussion? 

Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Friday, January 11, 2008 10:53 AM
To: [email protected]
Subject: Re: Planetarium ceilings

I would place a single EC concealed head at the top dead center of the dome
with additional heads outside the dome lower edge which will overlap the EC
to provide full coverage at the floor. The "Projectors are usually centered
below the dome so they can apply rotation to their presentations. The light
projecting onto the single EC coverplate, will have very little if any
distortion since the light source is directly below it. Additionally
remember these are usually "Visual Displays or Representations" and not
necessarily "Scientifically Accurate" If the shape of the cover plate does
move star HGF-3752-1 one million light years out of position, will it even
be noticeable to the unaided human eye? Planetariums give the visual
"Effect" of standing in place an looking out into space, not the reality.

My 2 cents and worth about 1/2 of that!

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Ron Greenman" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, January 11, 2008 8:14 AM
Subject: Re: Planetarium ceilings


> Allan,
>
> My very limited experience with this type of operation is that any
> foreign object on the dome will be verboten. You'd be introducing a
> plane, albeit small, to a curved surface and that will throw the
> projection slightly off (that is unless you can guarantee that at no
> time will any simulated heavenly body be projected so as to reflect
> off of one of these planes--the astro-physicists can probably write a
> program that will predict every possible permutation but my nerdy
> sense is starting to tingle). Considering our typical response to
> Hollywood how do you think an astronomy geek/planetarium nerd (I wish
> you could write nerd the way Wolfgang Rhinecastle says it) will
> respond to a few foreign bodies on his dome? I don't think the EOR's
> solution has any elegance but any alternative solution will need to
> avoid putting stuff on the reflective surface of the dome.
>
> On Jan 11, 2008 5:03 AM, Allan Seidel <[EMAIL PROTECTED]> wrote:
>> Right. The dome is white, but it may be some special white.
>>
>>
>> On Jan 11, 2008, at 6:31 AM, Todd Williams - FPDC wrote:
>>
>> > Allan,
>> >
>> > Why not consider having the plates factory painted to match the
>> > color of the dome? It is expensive (I think) but the client might
>> > be willing to spring for it for this situation. I'd get a price for
>> > 6 or 7 plates (spares would be good) and let them make the decision.
>> >
>> >
>> > At 11:57 PM 1/10/2008, you wrote:
>> >> Thanks for the responses.  Neither one of these approaches would be
>> >> my first choice. I now know where the Architect got the idea that
>> >> sidewalls at the dome base and sprinklers also above the dome is an
>> >> "accepted" solution! I can see the deluge as remotely possible, if
>> >> the detection can work and the system never goes false, except that
>> >> there is no easy way to get back up to the outside surface of the
>> >> dome for detector maintenance. Sounds like a job for Protecto-wire
>> >> maybe? I am in favor of a simple wet system using four flat white
>> >> Viking Mirages at about 2 o'clock high (2 feet to 3 feet below the
>> >> dome top). The dome radius is too tight for three ECs to work. This
>> >> is an existing planetarium, so a fused cover plate (hot coffee works
>> >> well to release a plate) has been sent with placement instructions
>> >> for the client to see if it really does anything to their projected
>> >> image. I hope it will be tolerable.
>> >>
>> >> Thanks again,
>> >> Allan Seidel
>> >> St. Louis, MO
>> >>
>> >>
>> >> On Jan 8, 2008, at 11:12 AM, Russell wrote:
>> >>
>> >>> Yep, sure was. Can't remember the exact size but something like a
>> >>> 30'
>> >>> diameter. Being on the deluge system, the sprinklers were open so
>> >>> ceiling
>> >>> was no consideration. The sidewalls were the only sprinklers on the
>> >>> deluge
>> >>> system. The system above the dome was wet. The detectors were above
>> >>> and
>> >>> attached to the dome skin. I don't recall what sort of detector's
>> >>> they were.
>> >>> Just for curiosity, I'll try to run it down, but it's been a long,
>> >>> long time
>> >>> and the mind is weak.
>> >>>
>> >>> Ron
>> >>>
>> >>> -----Original Message-----
>> >>> From: [EMAIL PROTECTED]
>> >>> [mailto:[EMAIL PROTECTED] On Behalf Of
>> >>> [EMAIL PROTECTED]
>> >>> Sent: Tuesday, January 08, 2008 10:53 AM
>> >>> To: [email protected]
>> >>> Subject: RE: Planetarium ceilings
>> >>>
>> >>> Deluge system?  Really?  Was that to protect against those simulated
>> >>> flaming meteors?
>> >>>
>> >>> How big was the room to allow sidewalls?  How did they install
>> >>> them in
>> >>> regards to mfgr and NFPA guidelines requiring max of 4-6 inches
>> >>> below
>> >>> ceilings?
>> >>>
>> >>> Was the deluge system above the dome and detectors above the dome?
>> >>>
>> >>>
>> >>> Craig L. Prahl, CET
>> >>> Fire Protection Group
>> >>> Mechanical Department
>> >>> CH2MHILL
>> >>> Lockwood Greene
>> >>> 1500 International Drive
>> >>> PO Box 491, Spartanburg, SC  29304-0491
>> >>> Direct - 864.599.4102
>> >>> Fax - 864.599.8439
>> >>> [EMAIL PROTECTED]
>> >>> http://www.lg.com
>> >>>
>> >>>
>> >>> -----Original Message-----
>> >>> From: [EMAIL PROTECTED]
>> >>> [mailto:[EMAIL PROTECTED] On Behalf Of
>> >>> Russell
>> >>> Sent: Tuesday, January 08, 2008 10:37 AM
>> >>> To: [email protected]
>> >>> Subject: RE: Planetarium ceilings
>> >>>
>> >>>
>> >>>
>> >>> I have been involved with this situation once. The engineer of
>> >>> record
>> >>> designed sidewall sprinklers 7'-0" A.F.F. 10'-0" max. spacing along
>> >>> the
>> >>> perimeter connected to a deluge system with detectors mounted at the
>> >>> domed portion on the outside of the dome. Don't remember what
>> >>> kind of
>> >>> detector he used to accomplish this. A wet pipe system was used
>> >>> at the
>> >>> roof deck throughout the area above the planetarium. All steel
>> >>> construction.
>> >>>
>> >>> Ron
>> >>>
>> >>>
>> >>>
>> >>> -----Original Message-----
>> >>> From: [EMAIL PROTECTED]
>> >>> [mailto:[EMAIL PROTECTED] On Behalf Of << 0
>> >>> o 0
>> >>> Sent: Tuesday, January 08, 2008 8:18 AM
>> >>> To: [email protected]
>> >>> Subject: RE: Planetarium ceilings
>> >>>
>> >>> Many moons ago I did one for Denison University, the EOR wanted
>> >>> vertical
>> >>> sidewalls around the perimeter of the dome. No heads in the
>> >>> planetarium
>> >>> ceiling. Not sure if that came from the manufacture of the dome,
>> >>> GC, EOR
>> >>> or the University. I don't remmber for sure but we may have had
>> >>> heads
>> >>> above the dome too.
>> >>>
>> >>>
>> >>> Bryan A. Dann
>> >>> Dannba Design Services, LLC
>> >>> Fire Sprinkler Designs
>> >>> Office: (740) 363-5878
>> >>> Cell: (740) 803-0967
>> >>> [EMAIL PROTECTED]
>> >>>
>> >>>
>> >>>
>> >>> -----Original Message-----
>> >>> From: [EMAIL PROTECTED]
>> >>> [mailto:[EMAIL PROTECTED] On Behalf Of Allan
>> >>> Seidel
>> >>> Sent: Monday, January 07, 2008 10:53 PM
>> >>> To: [email protected]
>> >>> Subject: Planetarium ceilings
>> >>>
>> >>>
>> >>> If I may tap into the sprinklerforum's years of experience, what is
>> >>> the
>> >>> typical practice for a planetarium ceiling? The planetarium in
>> >>> question
>> >>> has a domed metal ceiling of about 25 feet in diameter. The ceiling
>> >>> material is essentially the same as that of a 12 x 24 metal pan
>> >>> ceiling
>> >>> with tiny holes, except that the pans are curved pie sections. The
>> >>> projector sits at the center and therefore projects normal to the
>> >>> dome's
>> >>> inner surface. It seems to me that three small diameter Viking flat
>> >>> concealed sprinklers would probably have a negligible, if
>> >>> noticeable at
>> >>> all, impact on the projected image. I doubt there would be any
>> >>> shadow
>> >>> because the image arrives normal to the surface.  Has anyone done
>> >>> one of
>> >>> these?
>> >>>
>> >>> Thanks,
>> >>> Allan Seidel
>> >>> St. Louis, MO
>> >>> _______________________________________________
>> >>> Sprinklerforum mailing list
>> >>> [email protected]
>> >>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >> _______________________________________________
>> >> Sprinklerforum mailing list
>> >> [email protected]
>> >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >>
>> >> To Unsubscribe, send an email to:Sprinklerforum-
>> >> [EMAIL PROTECTED]
>> >> (Put the word unsubscribe in the subject field)
>> >
>> > Todd G. Williams, PE
>> > Fire Protection Design/Consulting
>> > Stonington, Connecticut
>> > www.fpdc.com
>> > 860.535.2080  _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]
>> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> > To Unsubscribe, send an email to:Sprinklerforum-
>> > [EMAIL PROTECTED]
>> > (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> -- 
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to