That, Bill, was my point. The planetarium operators are fuss-budgets
and consider their accuracy to be as important and realistic as the
engineers that believe six decimal place mathematical constructs based
upon whole numbers gathered during a point-in-time test on a dynamic
system are dead accurate. And Thom, those projectors project every
"star" along a radian so each point of light is as close as you can
get to the equivalent of a right angle on a curved surface. I think
Todd brought this up in his first post when suggesting the, I think I
remember him saying four, flat plates.

On Jan 11, 2008 9:21 AM, Bill Minkel <[EMAIL PROTECTED]> wrote:
> Why inject practical reality into the discussion?
>
>
> Bill Minkel, Designer
> Western States Fire Protection, Dallas
> NFPA Member #2578666
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
> Sent: Friday, January 11, 2008 10:53 AM
> To: [email protected]
>
> Subject: Re: Planetarium ceilings
>
> I would place a single EC concealed head at the top dead center of the dome
> with additional heads outside the dome lower edge which will overlap the EC
> to provide full coverage at the floor. The "Projectors are usually centered
> below the dome so they can apply rotation to their presentations. The light
> projecting onto the single EC coverplate, will have very little if any
> distortion since the light source is directly below it. Additionally
> remember these are usually "Visual Displays or Representations" and not
> necessarily "Scientifically Accurate" If the shape of the cover plate does
> move star HGF-3752-1 one million light years out of position, will it even
> be noticeable to the unaided human eye? Planetariums give the visual
> "Effect" of standing in place an looking out into space, not the reality.
>
> My 2 cents and worth about 1/2 of that!
>
> Thom McMahon
> Firetech, Inc.
> 2560 Copper Ridge Dr
> Steamboat Springs, CO 80488-2136
> Tel: 970-879-7952
> Fax: 970-879-7926
> ----- Original Message -----
> From: "Ron Greenman" <[EMAIL PROTECTED]>
> To: <[email protected]>
> Sent: Friday, January 11, 2008 8:14 AM
> Subject: Re: Planetarium ceilings
>
>
> > Allan,
> >
> > My very limited experience with this type of operation is that any
> > foreign object on the dome will be verboten. You'd be introducing a
> > plane, albeit small, to a curved surface and that will throw the
> > projection slightly off (that is unless you can guarantee that at no
> > time will any simulated heavenly body be projected so as to reflect
> > off of one of these planes--the astro-physicists can probably write a
> > program that will predict every possible permutation but my nerdy
> > sense is starting to tingle). Considering our typical response to
> > Hollywood how do you think an astronomy geek/planetarium nerd (I wish
> > you could write nerd the way Wolfgang Rhinecastle says it) will
> > respond to a few foreign bodies on his dome? I don't think the EOR's
> > solution has any elegance but any alternative solution will need to
> > avoid putting stuff on the reflective surface of the dome.
> >
> > On Jan 11, 2008 5:03 AM, Allan Seidel <[EMAIL PROTECTED]> wrote:
> >> Right. The dome is white, but it may be some special white.
> >>
> >>
> >> On Jan 11, 2008, at 6:31 AM, Todd Williams - FPDC wrote:
> >>
> >> > Allan,
> >> >
> >> > Why not consider having the plates factory painted to match the
> >> > color of the dome? It is expensive (I think) but the client might
> >> > be willing to spring for it for this situation. I'd get a price for
> >> > 6 or 7 plates (spares would be good) and let them make the decision.
> >> >
> >> >
> >> > At 11:57 PM 1/10/2008, you wrote:
> >> >> Thanks for the responses.  Neither one of these approaches would be
> >> >> my first choice. I now know where the Architect got the idea that
> >> >> sidewalls at the dome base and sprinklers also above the dome is an
> >> >> "accepted" solution! I can see the deluge as remotely possible, if
> >> >> the detection can work and the system never goes false, except that
> >> >> there is no easy way to get back up to the outside surface of the
> >> >> dome for detector maintenance. Sounds like a job for Protecto-wire
> >> >> maybe? I am in favor of a simple wet system using four flat white
> >> >> Viking Mirages at about 2 o'clock high (2 feet to 3 feet below the
> >> >> dome top). The dome radius is too tight for three ECs to work. This
> >> >> is an existing planetarium, so a fused cover plate (hot coffee works
> >> >> well to release a plate) has been sent with placement instructions
> >> >> for the client to see if it really does anything to their projected
> >> >> image. I hope it will be tolerable.
> >> >>
> >> >> Thanks again,
> >> >> Allan Seidel
> >> >> St. Louis, MO
> >> >>
> >> >>
> >> >> On Jan 8, 2008, at 11:12 AM, Russell wrote:
> >> >>
> >> >>> Yep, sure was. Can't remember the exact size but something like a
> >> >>> 30'
> >> >>> diameter. Being on the deluge system, the sprinklers were open so
> >> >>> ceiling
> >> >>> was no consideration. The sidewalls were the only sprinklers on the
> >> >>> deluge
> >> >>> system. The system above the dome was wet. The detectors were above
> >> >>> and
> >> >>> attached to the dome skin. I don't recall what sort of detector's
> >> >>> they were.
> >> >>> Just for curiosity, I'll try to run it down, but it's been a long,
> >> >>> long time
> >> >>> and the mind is weak.
> >> >>>
> >> >>> Ron
> >> >>>
> >> >>> -----Original Message-----
> >> >>> From: [EMAIL PROTECTED]
> >> >>> [mailto:[EMAIL PROTECTED] On Behalf Of
> >> >>> [EMAIL PROTECTED]
> >> >>> Sent: Tuesday, January 08, 2008 10:53 AM
> >> >>> To: [email protected]
> >> >>> Subject: RE: Planetarium ceilings
> >> >>>
> >> >>> Deluge system?  Really?  Was that to protect against those simulated
> >> >>> flaming meteors?
> >> >>>
> >> >>> How big was the room to allow sidewalls?  How did they install
> >> >>> them in
> >> >>> regards to mfgr and NFPA guidelines requiring max of 4-6 inches
> >> >>> below
> >> >>> ceilings?
> >> >>>
> >> >>> Was the deluge system above the dome and detectors above the dome?
> >> >>>
> >> >>>
> >> >>> Craig L. Prahl, CET
> >> >>> Fire Protection Group
> >> >>> Mechanical Department
> >> >>> CH2MHILL
> >> >>> Lockwood Greene
> >> >>> 1500 International Drive
> >> >>> PO Box 491, Spartanburg, SC  29304-0491
> >> >>> Direct - 864.599.4102
> >> >>> Fax - 864.599.8439
> >> >>> [EMAIL PROTECTED]
> >> >>> http://www.lg.com
> >> >>>
> >> >>>
> >> >>> -----Original Message-----
> >> >>> From: [EMAIL PROTECTED]
> >> >>> [mailto:[EMAIL PROTECTED] On Behalf Of
> >> >>> Russell
> >> >>> Sent: Tuesday, January 08, 2008 10:37 AM
> >> >>> To: [email protected]
> >> >>> Subject: RE: Planetarium ceilings
> >> >>>
> >> >>>
> >> >>>
> >> >>> I have been involved with this situation once. The engineer of
> >> >>> record
> >> >>> designed sidewall sprinklers 7'-0" A.F.F. 10'-0" max. spacing along
> >> >>> the
> >> >>> perimeter connected to a deluge system with detectors mounted at the
> >> >>> domed portion on the outside of the dome. Don't remember what
> >> >>> kind of
> >> >>> detector he used to accomplish this. A wet pipe system was used
> >> >>> at the
> >> >>> roof deck throughout the area above the planetarium. All steel
> >> >>> construction.
> >> >>>
> >> >>> Ron
> >> >>>
> >> >>>
> >> >>>
> >> >>> -----Original Message-----
> >> >>> From: [EMAIL PROTECTED]
> >> >>> [mailto:[EMAIL PROTECTED] On Behalf Of << 0
> >> >>> o 0
> >> >>> Sent: Tuesday, January 08, 2008 8:18 AM
> >> >>> To: [email protected]
> >> >>> Subject: RE: Planetarium ceilings
> >> >>>
> >> >>> Many moons ago I did one for Denison University, the EOR wanted
> >> >>> vertical
> >> >>> sidewalls around the perimeter of the dome. No heads in the
> >> >>> planetarium
> >> >>> ceiling. Not sure if that came from the manufacture of the dome,
> >> >>> GC, EOR
> >> >>> or the University. I don't remmber for sure but we may have had
> >> >>> heads
> >> >>> above the dome too.
> >> >>>
> >> >>>
> >> >>> Bryan A. Dann
> >> >>> Dannba Design Services, LLC
> >> >>> Fire Sprinkler Designs
> >> >>> Office: (740) 363-5878
> >> >>> Cell: (740) 803-0967
> >> >>> [EMAIL PROTECTED]
> >> >>>
> >> >>>
> >> >>>
> >> >>> -----Original Message-----
> >> >>> From: [EMAIL PROTECTED]
> >> >>> [mailto:[EMAIL PROTECTED] On Behalf Of Allan
> >> >>> Seidel
> >> >>> Sent: Monday, January 07, 2008 10:53 PM
> >> >>> To: [email protected]
> >> >>> Subject: Planetarium ceilings
> >> >>>
> >> >>>
> >> >>> If I may tap into the sprinklerforum's years of experience, what is
> >> >>> the
> >> >>> typical practice for a planetarium ceiling? The planetarium in
> >> >>> question
> >> >>> has a domed metal ceiling of about 25 feet in diameter. The ceiling
> >> >>> material is essentially the same as that of a 12 x 24 metal pan
> >> >>> ceiling
> >> >>> with tiny holes, except that the pans are curved pie sections. The
> >> >>> projector sits at the center and therefore projects normal to the
> >> >>> dome's
> >> >>> inner surface. It seems to me that three small diameter Viking flat
> >> >>> concealed sprinklers would probably have a negligible, if
> >> >>> noticeable at
> >> >>> all, impact on the projected image. I doubt there would be any
> >> >>> shadow
> >> >>> because the image arrives normal to the surface.  Has anyone done
> >> >>> one of
> >> >>> these?
> >> >>>
> >> >>> Thanks,
> >> >>> Allan Seidel
> >> >>> St. Louis, MO
> >> >>> _______________________________________________
> >> >>> Sprinklerforum mailing list
> >> >>> [email protected]
> >> >>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >> _______________________________________________
> >> >> Sprinklerforum mailing list
> >> >> [email protected]
> >> >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >>
> >> >> To Unsubscribe, send an email to:Sprinklerforum-
> >> >> [EMAIL PROTECTED]
> >> >> (Put the word unsubscribe in the subject field)
> >> >
> >> > Todd G. Williams, PE
> >> > Fire Protection Design/Consulting
> >> > Stonington, Connecticut
> >> > www.fpdc.com
> >> > 860.535.2080  _______________________________________________
> >> > Sprinklerforum mailing list
> >> > [email protected]
> >> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >
> >> > To Unsubscribe, send an email to:Sprinklerforum-
> >> > [EMAIL PROTECTED]
> >> > (Put the word unsubscribe in the subject field)
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> >> (Put the word unsubscribe in the subject field)
> >>
> >
> >
> >
> > --
> > Ron Greenman
> > at home....
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
> >
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....