Allan, This thing has intrigued me now. I do think that the deluge sidewalls may be the best arrangement for distribution but the detection scheme is weak. In another life I've been up above one of these domes doing inspections and it's no fun. I think I would spec an aspirating detection system here with the detector at a convenient location and the piping parallel to the sprinkler piping with sampling ports at the head locations. These detectors are smart and can be trained to discern between normal ambient particulates in the air and abnormal conditions. They can be trained to do this by day and time of day so that the sensitivity is X before the place opens when the dust in the air is low, goes to Y after opening due to the increased traffic and stirring up of the air, back to X after closing and after the dust has settled, to Z when the cleaning crew arrives and back to X after they leave. Since you're not worried about very early detection but rather normal QR you can set the sensitivity low to achieve what would be delayed response for this type of device but normal response for a light hazard sprinkler. These devices also monitor themselves for deviations caused by heir own age or particulate build-up in the filters and let you know when the latter needs attention. This would help alleviate some concern about false trips. If you're still worried you could use the type of releasing scheme the wonder gas boys do that relies on two separate initiating events (concurrence of dual but separate sampling). Of course all of this increases complexity which entails higher installation costs and the subsequent increased IT&M costs but these smart detectors are more reliable (unless completely neglected) than any spot detector scheme. Just a couple of thoughts for you. If this solution appeals to you and your client I'll let you know where to send the check :-)
On 1/11/08, Allan Seidel <[EMAIL PROTECTED]> wrote: > Actually the curve for this dome is too tight for an EC, even when > considering the actual deflector location. In other words the dome > itself violates the EC obstruction rules. I do agree that the > parallax error of the cover plate, which may be that it is called, > probably ain't noticeable. If they are taking measurements, this is a > university by the way, then maybe it would be educational for the > students to measure the error. They can always rotate the image off > the plate as what would happen automatically with time. I am > undoubtedly ignorant about this when I believe this is a matter of > some tiny dots on a black background. > > Allan Seidel > St. Louis, MO > > > On Jan 11, 2008, at 10:53 AM, Thom McMahon wrote: > > > I would place a single EC concealed head at the top dead center of > > the dome with additional heads outside the dome lower edge which > > will overlap the EC to provide full coverage at the floor. The > > "Projectors are usually centered below the dome so they can apply > > rotation to their presentations. The light projecting onto the > > single EC coverplate, will have very little if any distortion since > > the light source is directly below it. Additionally remember these > > are usually "Visual Displays or Representations" and not > > necessarily "Scientifically Accurate" If the shape of the cover > > plate does move star HGF-3752-1 one million light years out of > > position, will it even be noticeable to the unaided human eye? > > Planetariums give the visual "Effect" of standing in place an > > looking out into space, not the reality. > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)