Wow - that question may open a can of worms.  I always assumed that
residential sprinklers used in a 13 design had to be calced per section
11.3.1 (2007; 11.2.3.5 in the 2002).  That section says to calc the 4 most
demanding sprinklers, even if they exist in 4 separate rooms.  I reasoned
that it was (in part) to make up for the lower density allowed for
residential sprinklers.  Well, the lower density is no longer allowed in a
13 design, so that reasoning is kaput.

In Greg's example (one sprinkler in a unit with self closing doors), the
incentive seems to be to install QR sprinklers instead of residential.
Then, by room design method, only 1 sprinkler is calced instead of 4.  Or
maybe the unit has 2 sprinklers, but it still has the impact of decreasing
pipe sizes.  

Since residential sprinklers used in a 13 design now must provide a minimum
.10 density, is there any reason (other than 13 doesn't seem to allow it)
that they shouldn't be allowed to be calced using the room design method?  

Ed Kramer
Littleton, CO




-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Thursday, January 24, 2008 4:15 PM
To: [email protected]
Subject: residential heads / 4 head calc

Can you use the most demanding room method when calculating residential
sprinklers in a Hotel per NFPA 13?

QR sprinklers where there is only one head in a motel room with self
closing doors?

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to