If your using residential heads it's the 4 most demanding sprinklers regardless of whether they are in the same room or not, see NFPA 13 2002 figure A.11.2.3.5.2. You could apply the room design method, per 11.2.3.3, if your not using residential heads.
Ryan Peterson Wayne Automatic Fire Sprinklers -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Thursday, January 24, 2008 6:15 PM To: [email protected] Subject: residential heads / 4 head calc Can you use the most demanding room method when calculating residential sprinklers in a Hotel per NFPA 13? QR sprinklers where there is only one head in a motel room with self closing doors? Thank you, Greg McGahan Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)