11.3.1.2. #2, 2007 13 is worded "over the design area" as opposed to
8.5.2.1.1 "protection area of coverage" per sxl and goes on to note
8.6.2.1.2 which states "shall be the area of the room divided by the number
of sprinklers" for small rooms.
Just my take on it.

Ron

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, January 25, 2008 10:18 AM
To: [email protected]
Subject: RE: residential heads / 4 head calc

Greg,
I don't see either "compartment" or "room" stated in either 02 or 07,
just the 4 hydraulically most demanding. I think that if you use the
"listed" area and pressures in your calc for the residential heads and
not the actual area, then it is no different than using extended
coverage QR sprinklers.  But then one would have to ask, why not use QR
to begin with?
Dewayne Martinez, CET
Design Build Fire Protection
[EMAIL PROTECTED]
  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Friday, January 25, 2008 6:53 AM
To: [email protected]
Subject: RE: residential heads / 4 head calc

Well, that is my point. Since the density is now .10 in order compensate
for the difference in property protection vs life safety protection, I
can not understand the difference in the stipulation between residential
and QR in this case.

In addition; 11.3.1 does not say "rooms" it says "compartments". A
compartment does not have to have ANY fire resistance and can have
openings, while a room "shall be enclosed with walls having a
fire-resistance rating equal to the water supply duration indicated in
Table 11.2.3.1.2". I feel that this is a significant difference and
therefore you should be able to use the room design method in this case.

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, January 25, 2008 6:21 AM
To: [email protected]
Subject: RE: residential heads / 4 head calc

Perhaps because you use the actual area of the residential sprinkler,
not the listed area, in the calculation process?
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Thursday, January 24, 2008 6:18 PM
To: [email protected]
Subject: RE: residential heads / 4 head calc

Wow - that question may open a can of worms.  I always assumed that
residential sprinklers used in a 13 design had to be calced per section
11.3.1 (2007; 11.2.3.5 in the 2002).  That section says to calc the 4
most demanding sprinklers, even if they exist in 4 separate rooms.  I
reasoned that it was (in part) to make up for the lower density allowed
for residential sprinklers.  Well, the lower density is no longer
allowed in a
13 design, so that reasoning is kaput.

In Greg's example (one sprinkler in a unit with self closing doors), the
incentive seems to be to install QR sprinklers instead of residential.
Then, by room design method, only 1 sprinkler is calced instead of 4.
Or maybe the unit has 2 sprinklers, but it still has the impact of
decreasing pipe sizes.  

Since residential sprinklers used in a 13 design now must provide a
minimum .10 density, is there any reason (other than 13 doesn't seem to
allow it) that they shouldn't be allowed to be calced using the room
design method?  

Ed Kramer
Littleton, CO




-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Thursday, January 24, 2008 4:15 PM
To: [email protected]
Subject: residential heads / 4 head calc

Can you use the most demanding room method when calculating residential
sprinklers in a Hotel per NFPA 13?

QR sprinklers where there is only one head in a motel room with self
closing doors?

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Internal Virus Database is out-of-date.
Checked by AVG Free Edition. 
Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007
1:39 PM
 

Internal Virus Database is out-of-date.
Checked by AVG Free Edition. 
Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007
1:39 PM
 