account for change in pipe type as required, don't count flow switch if
over 2" pipe, gauge doesn't enter flow, so no loss

ed
aero
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of RFI -
Bismarck
Sent: Friday, January 25, 2008 12:35 PM
To: [email protected]
Subject: Calculation Input...

 

Question...

What has / have any of the forum designers done in relation to adding a
"length" or "psi loss" to the hydraulics for a riser manifold (such as
Tyco's Model 513).  Looking through the spec' sheet, I can't find
anything that would give me something - unless I'm blind... and it is
Friday!  I know that it would be fairly 'minimal' with only the paddle
and the gage impeding the water characteristics.  Any input would be
greatly appreciated.

 

Thanks!

 

RFI Chuck


No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.516 / Virus Database: 269.19.11/1243 - Release Date:
1/25/2008
11:24 AM
 
  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to