Actually, all residential are Fast Response (QR) but not all Fast Response (QR) 
are residential.

The consideration is as much a function of spray patterns, coverages, sprinkler 
placement, discharge characteristics, etc. when determining which sprinklers, 
and by default, which design paramters to utilize. You can not just interchange 
them nor their design parameters based on one or two considerations.

If you choose to utilize residential, you must also utilize the residential 
design parameters.
If you choose to utilize quick-response (non-residential), you must then 
utilize the area/density method, room design method, corridor calculation 
method, etc (whatever and where ever it applies or is required) to 
design/calculate your system.

They are not interchangeable, in my opinion, unless the NFPA standards 
specifically directs you to "special" allowances for their use.

Thanks,

Ray Vance
Chief Engineering Tech.
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com


 

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack, SET
Sent: Friday, January 25, 2008 12:15 PM
To: [email protected]
Subject: RE: residential heads / 4 head calc

I believe they are FAST response, but not listed as QR.  However, I could be 
wrong on that.  Just because it has a 3mm bulb does not make it a QR sprinkler. 
 So, if they are Fast response, then Greg's question is very valid.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of å... ....
Sent: Friday, January 25, 2008 9:33 AM
To: [email protected]
Subject: residential heads / 4 head calc

is there a residential sprinkler that is NOT QR.
I know there are other criteria in the design of residential sprinklers (like 
higher throw), but I thought all were QR, at least for the point of making this 
dumb question here and now.

scot deal
excelsior fire
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

__________ NOD32 2822 (20080125) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to