A single use structure has been divided into 3 buildings because of
occupancy and construction type issues related to the IBC.  Horizontal
exits are provided and this means the building cannot be evacuated
simultaneously using the stair widths available.

Question - Are separate sprinkler zones required for each building?  I
believe the answer is yes but I can't find a code reference that spells
this out in black and white.  It seems if the sprinkler zones cross over
the building boundary the fire alarm system will not be able to operate
the correct evacuation signals.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell