2003 IBC 903.4.3 Floor control valves. Approved supervised indicating control valves shall be provided at the point of connection to the riser on each floor in high-rise buildings.
Joe Burtell, SET, CFPS Burtell Fire Protection, Inc. [EMAIL PROTECTED] www.burtellfire.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer Sent: Thursday, February 14, 2008 8:55 AM To: [email protected] Subject: RE: Check valve on floor control assembly Cliff, I'm not aware of anything in 13 that requires the check valve. Also worth noting, nothing in 13 requires that each floor has its own control valve (except for high rises, I think). I tried to find the section that requires the control valves in high rises but couldn't. Anyone know if it's been removed, or am I just missing it? Ed Kramer Littleton, CO > -----Original Message----- > From: [EMAIL PROTECTED] [mailto:sprinklerforum- > [EMAIL PROTECTED] On Behalf Of Cliff Whitfield > Sent: Wednesday, February 13, 2008 1:50 PM > To: [email protected] > Subject: Check valve on floor control assembly > > NFPA 14 requires a check valve on a floor control assembly for a > connection > to a standpipe that is part of a combined system. (6.3.5.1 2007 ed) > Does > this requirement cross over to NFPA 13 for a riser in a multi-story > building > that is not actually a standpipe? Like for a 3-story bldg that isn't > high > enough to require a standpipe. > > > > I understand that it would be a good idea for the same reasons it is > required on a standpipe but is it actually a requirement? > > > > Cliff Whitfield, SET > > Fire Design, Inc. > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:Sprinklerforum- > [EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)