If it meets the criteria in NFPA for omitting sprinklers in a
concealed space, then I think you could omit them. The standard says
nothing about what is above or below the space. The problem with the
building in MA is that some of the older ceiling is missing, exposing
wood framing, so FM wants sprinklers everywhere. Just out of
curiosity, is the combustible space with the sprinklers above the
void space accessible for maintenance or repair?
At 02:22 PM 2/19/2008, you wrote:
Todd,
This is not an FM job, so would you place the sprinklers in the voids? It
seems like extra work and unnecessary to me. What does anyone else have to
say?
Thanks,
BK
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:sprinklerforum- [EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Monday, February 18, 2008 5:08 PM
To: [email protected]
Subject: Re: Ceiling Void Space
If FM Global has anything to say about it, yes. There is a building
in MA with several floors of this type of thing that FM wants
protected. I gave them a quote for drawings (100% survey), but they
didn't feel like burning my mortgage.
At 06:54 PM 2/18/2008, you wrote:
|------------------------------------------
|
|
| NONCOMBUSTIBLE SPACE
|___________________________________________
| X = sprinkler @ ceiling
| 10" DEEP X 8' LONG VOID
| B/TWN CEILINGS
|___________________________
|
|
NONCOMBUSTIBLE SPACE |
|
-----------------------------
X = sprinkler @ ceiling
If this picture turned out, would sprinklers be required to be place
In the "void" between the upper and lower ceilings?
The materials are ACT ceiling above w/ a gyp board ceiling below.
The soffit type structure is completely wrapped, and there are no
Openings into the noncombustible space beyond.
Thank you,
Bob Knight, CET
(208) 495-2057
[EMAIL PROTECTED]
www.firebyknight.com
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.516 / Virus Database: 269.20.8/1287 - Release Date: 2/19/2008
10:55 AM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)