I guess that kills the idea of windows. Would this really apply for things like omitting sprinklers in hotel bathrooms but being able to see them from the hall or bedroom?

At 06:05 PM 2/19/2008, you wrote:
I was taught that a person in a sprinklered area should never be able to look into an unsprinklered area. That is the rule of thumb that coincides with the prescriptive rules in NFPA 13 of "protected throughout" unless omission of sprinklers is permitted. The area you described does not qualify for omission of sprinklers.

  J. Scott Mitchell, P.E.

Bob Knight <[EMAIL PROTECTED]> wrote:
  -----Original Message-----
From: [EMAIL PROTECTED]
[mailto:sprinklerforum- [EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Monday, February 18, 2008 5:08 PM
To: [email protected]
Subject: Re: Ceiling Void Space

If FM Global has anything to say about it, yes. There is a building
in MA with several floors of this type of thing that FM wants
protected. I gave them a quote for drawings (100% survey), but they
didn't feel like burning my mortgage.

At 06:54 PM 2/18/2008, you wrote:
|------------------------------------------
|
|
| NONCOMBUSTIBLE SPACE
|___________________________________________
| X = sprinkler @ ceiling
| 10" DEEP X 8' LONG VOID
| B/TWN CEILINGS
|___________________________
|
|
NONCOMBUSTIBLE SPACE |
|
-----------------------------
X = sprinkler @ ceiling

If this picture turned out, would sprinklers be required to be place
In the "void" between the upper and lower ceilings?
The materials are ACT ceiling above w/ a gyp board ceiling below.
The soffit type structure is completely wrapped, and there are no
Openings into the noncombustible space beyond.

Thank you,

Bob Knight, CET
(208) 495-2057
[EMAIL PROTECTED]
www.firebyknight.com



---------------------------------
Looking for last minute shopping deals?  Find them fast with Yahoo! Search.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to