At one of my AHJ stops, an architect had his way with a nature center/museum
and by all indications probably went one toke over the line. One of the
features was a row of windows in the exterior wall just under the EXPOSED roof
deck. Just below the windows and coming out horizontally was a sheetrock
finished (the top of the ceiling assembly was gypsum) ceiling assembly for the
large display cases / side rooms below. Then there were short (~3') walls
extending vertically from this ceiling assembly to the roof deck at about 5'
intervals. Described another way, these were 3' tall by 5' wide sheetrock
channels 10' deep with a window on one end and an opening to the occupied space
on the other end. Could the roof deck sprinkler spacing be measured from the
"inside" end of the channel or did it have to extend to the window? -- was the
contractor's question. My answer was that it had to extend to the window
because the space between the window and the "inside" end of the channel
did not qualify for omission of sprinklers.
Had the sprinkler spacing been permitted to stop at the inside end of the
channel, then I could have stood in a sprinklered area and been able to look
into an unsprinklered area.
I think the intent of NFPA 13 with this and similar issues is that we are not
only protecting the floor area, but also the building structure.
J. Scott Mitchell, P.E.
Cliff Whitfield <[EMAIL PROTECTED]> wrote:
Okay. Let's not get another one started today! He said "unless omission of
sprinklers is permitted".
I still can't picture what Bob has described. From what I see (at least in
my mind), it looks to me like the void would not require sprinklers.
Cliff
---------------------------------