Elevation still affects the pressure in a closed system.  If the water
is static in a pressurized system the pressure is the same throughout
the system only at a constant elevation.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Thursday, February 28, 2008 11:55 AM
To: [email protected]
Subject: BASIC HYDRAULICS

Someone educate me or re-educate me on basic hydraulics, engineering not
necessarily sprinkler hydraulics. I understand the difference between
static pressure and residual pressure while flowing some amount and how
gravity losses come into play with increasing elevation. However I have
the notion that a closed system when pressurized has equal pressure thru
the entire system such as when testing a sprinkler system at 200 psi.
The pressure in the closed system pumped up to 200 psi is 200 psi
throughout regardless of elevation?
 
Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to