Like the pressure at the bottom of the sea.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Thursday, February 28, 2008 1:32 PM
To: [email protected]
Subject: Re: BASIC HYDRAULICS

Elevation still comes into play. It is based on the weight of water,
which is independent of other forces that may create pressure.


At 11:55 AM 2/28/2008, you wrote:
>Someone educate me or re-educate me on basic hydraulics, engineering
not
>necessarily sprinkler hydraulics. I understand the difference between
static
>pressure and residual pressure while flowing some amount and how
gravity
>losses come into play with increasing elevation. However I have the
notion
>that a closed system when pressurized has equal pressure thru the
entire
>system such as when testing a sprinkler system at 200 psi. The pressure
in
>the closed system pumped up to 200 psi is 200 psi throughout regardless
of
>elevation?
>
>Bill Minkel, Designer
>Western States Fire Protection, Dallas
>NFPA Member #2578666
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email
to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to