Elevation still comes into play. It is based on the weight of water, which is independent of other forces that may create pressure.

At 11:55 AM 2/28/2008, you wrote:
Someone educate me or re-educate me on basic hydraulics, engineering not
necessarily sprinkler hydraulics. I understand the difference between static
pressure and residual pressure while flowing some amount and how gravity
losses come into play with increasing elevation. However I have the notion
that a closed system when pressurized has equal pressure thru the entire
system such as when testing a sprinkler system at 200 psi. The pressure in
the closed system pumped up to 200 psi is 200 psi throughout regardless of
elevation?

Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com