I did four Kohls in Nashville, TN a few years ago & no in-rack sprinklers were used to my recollection. My recall is the .45/2000 you mention with a K-25 or something similar upright storage sprinkler?
Bill Minkel, Designer Western States Fire Protection, Dallas NFPA Member #2578666 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell Sent: Thursday, February 28, 2008 1:43 PM To: [email protected] Subject: Kohl's Has anyone done a Kohl's store lately? In particular I am interested what was done in the storage room. I asked some questions about the storage and I get the usual, we've never done that before response. Here is what they have: 17' to deck 15' of storage, 2' wide solid shelf racks, they are really shelf storage but it over the 30" limit due to back to back configuration Class I-V and Group A plastics Cartoned, unexpanded I let them know that due to the solid shelf they will need 1 level of in-rack sprinklers. They gave a .45/2000 which works fine without solid shelves. Any opinions? Joe Burtell, SET, CFPS Burtell Fire Protection, Inc. [EMAIL PROTECTED] www.burtellfire.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)