In the last Kohl's I did, the shelves were not back-to-back, so I considered them as shelves. The trickiest part of that job was the almost unnoticeable light baffles around the exterior.

At 02:43 PM 2/28/2008, you wrote:
Has anyone done a Kohl's store lately? In particular I am interested what
was done in the storage room. I asked some questions about the storage and I
get the usual, we've never done that before response. Here is what they
have:
17' to deck
15' of storage, 2' wide solid shelf racks, they are really shelf storage but
it over the 30" limit due to back to back configuration
Class I-V and Group A plastics Cartoned, unexpanded

I let them know that due to the solid shelf they will need 1 level of
in-rack sprinklers. They gave a .45/2000 which works fine without solid
shelves. Any opinions?



Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to