Kohl's had a detailed spec and the sprinkler protection was per their
Engineer of Record & possibly insurance carrier. We were Sprinkler
Contractors, not Engineers so our procedure was to design to their specs and
adjust if any of the local AHJ's objected as I recall. We did not suggest to
them alternatives since we were not consultants and they did not ask our
advice, we were subs to the general contractor. Also Nashville at that time
was still under 13-1996 I think? If Kohl's showed In-racks we installed
them, my recollection however is that we had upright storage sprinklers
only. Heck of a demand as I recall I even had to run some 8" main in one
because of that, with 1 1/4" armovers to boot in the main store area. If you
are doing the work then bid it as you see it.

Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Thursday, February 28, 2008 2:11 PM
To: [email protected]
Subject: RE: Kohl's

How did you get around these sections of NFPA 13 02'?

12.3.1.9.1 Where solid shelving in single-, double-, and multiple-row racks
exceeds 20 ft2 but does not exceed 64 ft2 in area, sprinklers shall not be
required below every shelf, but shall be installed at the ceiling and below
shelves at intermediate levels not more than 6 ft (2 m) apart vertically.
(See Section C.11.)

12.3.1.9.2 Where solid shelving in single-, double-, and multiple-row racks
exceeds 64 ft2 in area or where the levels of storage exceed 6 ft (2 m),
sprinklers shall be installed at the ceiling and below each level of
shelving.

This falls within the first one.

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel
Sent: Thursday, February 28, 2008 12:53 PM
To: [email protected]
Subject: RE: Kohl's

I did four Kohls in Nashville, TN a few years ago & no in-rack sprinklers
were used to my recollection. My recall is the .45/2000 you mention with a
K-25 or something similar upright storage sprinkler?


Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Thursday, February 28, 2008 1:43 PM
To: [email protected]
Subject: Kohl's

Has anyone done a Kohl's store lately? In particular I am interested what
was done in the storage room. I asked some questions about the storage and I
get the usual, we've never done that before response. Here is what they
have:
17' to deck
15' of storage, 2' wide solid shelf racks, they are really shelf storage but
it over the 30" limit due to back to back configuration Class I-V and Group
A plastics Cartoned, unexpanded

I let them know that due to the solid shelf they will need 1 level of
in-rack sprinklers. They gave a .45/2000 which works fine without solid
shelves. Any opinions?



Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to