I beg to differ I see the standard as clear in that that the structure must be capable of holding the filled pipe plus 250 pounds. The hanger section has the additional requirement of the 5 times the filled weight of the pipe. They are separate requirements in separate sections. 9.2.1.3.1 is in the section called building structure and it seems clear that the section is refffering to the structure at the point of hanging.
9.2.1.3* Building Structure. 9.2.1.3.1 Sprinkler piping shall be substantially supported from the building structure, which must support the added load of the water-filled pipe plus a minimum of 250 lb (114 kg) applied at the point of hanging. 9.1.1.2 Hangers certified by a registered professional engineer to include all of the following shall be an acceptable alternative to the requirements of Section 9.1: (1) Hangers shall be designed to support five times the weight of the water-filled pipe plus 250 lb (114 kg) at each point of piping support. (2) These points of support shall be adequate to support the system. (3) The spacing between hangers shall not exceed the value given for the type of pipe as indicated in Table 9.2.2.1. (4) Hanger components shall be ferrous. (5) Detailed calculations shall be submitted, when required by the reviewing authority, showing stresses developed in hangers, piping, and fittings and safety factors allowed. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Denhardt Sent: Friday, February 29, 2008 1:21 PM To: [email protected] Subject: RE: Sammy express hangers Dave - I think you are reading too much into the standard. The hangar assembly must meet that requirement. The structure only has to support the actual weight. You do not need to design the building's structure to five times the weight of the water-filled piping plus 250 pounds. Hope this helps, John John August Denhardt, P.E. Strickland Fire Protection Incorporated 5113 Berwyn Road College Park, Maryland 20740 Office Telephone Number: 301-474-1136 Mobile Telephone Number: 301-343-1457 FIRE SPRINKLERS SAVE LIVES -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of David M. Canham Sent: Friday, February 29, 2008 12:21 PM To: [email protected] Subject: RE: Sammy express hangers Unless the roof or Z-purlin can handle 250 punds plus the pipe the code has not been meet. 9.2.1.3.1 Sprinkler piping shall be substantially supported from the building structure, which must support the added load of the water-filled pipe plus a minimum of 250 lb (114 kg) applied at the point of hanging. Dave Canham Fire Systems Solutions -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Friday, February 29, 2008 11:26 AM To: [email protected] Subject: RE: Sammy express hangers Dewayne, The last project, which I think was similar to your situation, we used Sammy side-winders on the Z-purlins. It was an ESFR project and I think we roughly calculated the load would be about 1.1 lbs/ft2 on average. We did have to check with structural to make sure the point loads could be handle for the cross main. I think they told me that 2-3 lbs is added for miscellaneous loads such as sprinklers, lights, HVAC. James L.(Jim) Roberts, PE/SET Fluor Corporation 100 Fluor Daniel Drive - C104F Greenville, SC 29607 864.281.5149 864.281.4916(Fax) "Steve Leyton" <[EMAIL PROTECTED]> Sent by: [EMAIL PROTECTED] 02/29/2008 10:39 AM Please respond to sprinklerforum To <[email protected]> cc Subject RE: Sammy express hangers There's no one answer Dewayne. Some roof decks can bear the load, some can't. That question should be referred to the project structural engineer of record. If the roof has structural concrete on it, which many do, it can often bear the load of branch piping and arm-overs. Some are so lightweight, they can't bear even the arm-overs. Steve Leyton Protection Design & Consulting -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dewayne Martinez Sent: Friday, February 29, 2008 7:09 AM To: [email protected] Subject: Sammy express hangers Has anyone run into problems with building inspectors when trying to use the Sammy express hanger in the roof deck. I have one telling me that "the metal decking is designed for the roofing materials and designed loads (rain, snow, etc.). That the design did not include other loads." Is this true? Thanks, Dewayne _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) ------------------------------------------------------------ The information transmitted is intended only for the person or entity to which it is addressed and may contain proprietary, business-confidential and/or privileged material. If you are not the intended recipient of this message you are hereby notified that any use, review, retransmission, dissemination, distribution, reproduction or any action taken in reliance upon this message is prohibited. If you received this in error, please contact the sender and delete the material from any computer. Any views expressed in this message are those of the individual sender and may not necessarily reflect the views of the company. ------------------------------------------------------------ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)