And let's not forget that the 250# we're talking about started out as a fat guy on a ladder falling and grabbing onto the pipe to save himself. Now look at OSHA and that FGOL should not be expecting anything that will not support a 6000# impact load to keep him from falling. He should also not be tied off to anything that can't take those impact loads (Sprinkler pipe, conduit, copper water lines, phone wire or CATV) I believe that there have been efforts to remove the 250# from the standard since OSHA would not allow this anyway, but so far it's still here. The old saying (especially with pre fab metal buildings) has always been "Just because the hanger will support your pipe doesn't automatically mean the structure will.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "John Denhardt" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, February 29, 2008 11:21 AM
Subject: RE: Sammy express hangers


Dave - I think you are reading too much into the standard.  The hangar
assembly must meet that requirement.  The structure only has to support
the actual weight.  You do not need to design the building's structure
to five times the weight of the water-filled piping plus 250 pounds.

Hope this helps,
John

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David M.
Canham
Sent: Friday, February 29, 2008 12:21 PM
To: [email protected]
Subject: RE: Sammy express hangers

Unless the roof or Z-purlin can handle 250 punds plus the pipe the code
has
not been meet.
9.2.1.3.1  Sprinkler piping shall be substantially supported from the
building structure, which must support the added load of the
water-filled
pipe plus a minimum of 250 lb (114 kg) applied at the point of hanging.

Dave Canham
Fire Systems Solutions

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, February 29, 2008 11:26 AM
To: [email protected]
Subject: RE: Sammy express hangers

Dewayne,

The last project, which I think was similar to your situation, we used
Sammy side-winders on the Z-purlins.  It was an ESFR project and I think

we roughly calculated the load would be about 1.1 lbs/ft2 on average.
We
did have to check with structural to make sure the point loads could be
handle for the cross main.  I think they told me that 2-3 lbs is added
for
miscellaneous loads such as sprinklers, lights, HVAC.

James L.(Jim) Roberts, PE/SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)





"Steve Leyton" <[EMAIL PROTECTED]>
Sent by:  [EMAIL PROTECTED]
02/29/2008 10:39 AM
Please respond to sprinklerforum

To
<[email protected]>
cc

Subject
RE: Sammy express hangers







There's no one answer Dewayne.   Some roof decks can bear the load, some
can't.    That question should be referred to the project structural
engineer of record.  If the roof has structural concrete on it, which
many do, it can often bear the load of branch piping and arm-overs.
Some are so lightweight, they can't bear even the arm-overs.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, February 29, 2008 7:09 AM
To: [email protected]
Subject: Sammy express hangers

Has anyone run into problems with building inspectors when trying to use
the Sammy express hanger in the roof deck.  I have one telling me that
"the metal decking is designed for the roofing materials and designed
loads (rain, snow, etc.). That the design did not include other loads."
Is this true?
Thanks,
Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person
or entity to which it is addressed and may contain
proprietary, business-confidential and/or privileged material.
If you are not the intended recipient of this message you are
hereby notified that any use, review, retransmission, dissemination,
distribution, reproduction or any action taken in reliance upon
this message is prohibited. If you received this in error, please
contact the sender and delete the material from any computer.

Any views expressed in this message are those of the individual
sender and may not necessarily reflect the views of the company.
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to