Thom,

It wasn't originally a fat guy. It was a regular guy and his toolbelt.
Now it probably will be a fat guy--and his toolbelt.

On 2/29/08, Thom McMahon <[EMAIL PROTECTED]> wrote:
> And let's not forget that the 250# we're talking about started out as a fat
>  guy on a ladder falling and grabbing onto the pipe to save himself. Now look
>  at OSHA and that FGOL should not be expecting anything that will not support
>  a 6000# impact load to keep him from falling. He should also not be tied off
>  to anything that can't take those impact loads (Sprinkler pipe, conduit,
>  copper water lines, phone wire or CATV)
>  I believe that there have been efforts to remove the 250# from the standard
>  since OSHA would not allow this anyway, but so far it's still here.
>  The old saying (especially with pre fab metal buildings) has always been
>  "Just because the hanger will support your pipe doesn't automatically mean
>  the structure will.
>
>
>  Thom McMahon
>  Firetech, Inc.
>  2560 Copper Ridge Dr
>  Steamboat Springs, CO 80488-2136
>  Tel: 970-879-7952
>  Fax: 970-879-7926
>
> ----- Original Message -----
>  From: "John Denhardt" <[EMAIL PROTECTED]>
>  To: <[email protected]>
>  Sent: Friday, February 29, 2008 11:21 AM
>  Subject: RE: Sammy express hangers
>
>
>  Dave - I think you are reading too much into the standard.  The hangar
>  assembly must meet that requirement.  The structure only has to support
>  the actual weight.  You do not need to design the building's structure
>  to five times the weight of the water-filled piping plus 250 pounds.
>
>  Hope this helps,
>  John
>
>  John August Denhardt, P.E.
>  Strickland Fire Protection Incorporated
>  5113 Berwyn Road
>  College Park, Maryland 20740
>  Office Telephone Number:  301-474-1136
>  Mobile Telephone Number:  301-343-1457
>  FIRE SPRINKLERS SAVE LIVES
>
>
>  -----Original Message-----
>  From: [EMAIL PROTECTED]
>  [mailto:[EMAIL PROTECTED] On Behalf Of David M.
>  Canham
>  Sent: Friday, February 29, 2008 12:21 PM
>  To: [email protected]
>  Subject: RE: Sammy express hangers
>
>  Unless the roof or Z-purlin can handle 250 punds plus the pipe the code
>  has
>  not been meet.
>  9.2.1.3.1  Sprinkler piping shall be substantially supported from the
>  building structure, which must support the added load of the
>  water-filled
>  pipe plus a minimum of 250 lb (114 kg) applied at the point of hanging.
>
>  Dave Canham
>  Fire Systems Solutions
>
>  -----Original Message-----
>  From: [EMAIL PROTECTED]
>  [mailto:[EMAIL PROTECTED] On Behalf Of
>  [EMAIL PROTECTED]
>  Sent: Friday, February 29, 2008 11:26 AM
>  To: [email protected]
>  Subject: RE: Sammy express hangers
>
>  Dewayne,
>
>  The last project, which I think was similar to your situation, we used
>  Sammy side-winders on the Z-purlins.  It was an ESFR project and I think
>
>  we roughly calculated the load would be about 1.1 lbs/ft2 on average.
>  We
>  did have to check with structural to make sure the point loads could be
>  handle for the cross main.  I think they told me that 2-3 lbs is added
>  for
>  miscellaneous loads such as sprinklers, lights, HVAC.
>
>  James L.(Jim) Roberts, PE/SET
>  Fluor Corporation
>  100 Fluor Daniel Drive - C104F
>  Greenville, SC 29607
>  864.281.5149
>  864.281.4916(Fax)
>
>
>
>
>
>  "Steve Leyton" <[EMAIL PROTECTED]>
>  Sent by:  [EMAIL PROTECTED]
>  02/29/2008 10:39 AM
>  Please respond to sprinklerforum
>
>  To
>  <[email protected]>
>  cc
>
>  Subject
>  RE: Sammy express hangers
>
>
>
>
>
>
>
>  There's no one answer Dewayne.   Some roof decks can bear the load, some
>  can't.    That question should be referred to the project structural
>  engineer of record.  If the roof has structural concrete on it, which
>  many do, it can often bear the load of branch piping and arm-overs.
>  Some are so lightweight, they can't bear even the arm-overs.
>
>  Steve Leyton
>  Protection Design & Consulting
>
>
>  -----Original Message-----
>  From: [EMAIL PROTECTED]
>  [mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
>  Martinez
>  Sent: Friday, February 29, 2008 7:09 AM
>  To: [email protected]
>  Subject: Sammy express hangers
>
>  Has anyone run into problems with building inspectors when trying to use
>  the Sammy express hanger in the roof deck.  I have one telling me that
>  "the metal decking is designed for the roofing materials and designed
>  loads (rain, snow, etc.). That the design did not include other loads."
>  Is this true?
>  Thanks,
>  Dewayne
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email
>  to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email
>  to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>
>  ------------------------------------------------------------
>  The information transmitted is intended only for the person
>  or entity to which it is addressed and may contain
>  proprietary, business-confidential and/or privileged material.
>  If you are not the intended recipient of this message you are
>  hereby notified that any use, review, retransmission, dissemination,
>  distribution, reproduction or any action taken in reliance upon
>  this message is prohibited. If you received this in error, please
>  contact the sender and delete the material from any computer.
>
>  Any views expressed in this message are those of the individual
>  sender and may not necessarily reflect the views of the company.
>  ------------------------------------------------------------
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email
>  to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email
>  to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....