NFPA 13 - 2007 

I would try Section 21.6: .30gpm/sq.ft. over 2500 sq.ft.  100 sq.ft. per
sprinkler maximum

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David
Phelan
Sent: Monday, March 10, 2008 1:51 PM
To: [email protected]
Subject: Fuel Tank Rooms

How does the group feel on the occupancy classification of a rated room
in a building that contains a 275 Gal #2 Fuel tank for the rooftop
generator?  The room is on the ground level and the tank is 130 feet
above on the roof.
   
  The architect is calling this a OH2 hazard and protecting the room
with a single K5.6 QR Head @ .18 over 1500 Ft2.  His reasoning is that
the tank is not combustible, just the product in it .......  Im leaning
towards a EH designation in the event of fire the fuel would be more
than capable of supporting combustion.  At the very least I dont see the
current configuration as being adequate.
   
  Thanks,
   
  Dave P.
  An AHJ in NJ
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to