OH2 sounds good to me. As long as the total amount of Class II in the room is less than the maximum allowable quantity per IFC the use of the room remains classified the same as the rest of the building. I believe the MAQ is 660 gallons before the occupancy would change to "H" requiring extra hazard sprinkler system.
Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of David Phelan Sent: Monday, March 10, 2008 10:51 AM To: [email protected] Subject: Fuel Tank Rooms How does the group feel on the occupancy classification of a rated room in a building that contains a 275 Gal #2 Fuel tank for the rooftop generator? The room is on the ground level and the tank is 130 feet above on the roof. The architect is calling this a OH2 hazard and protecting the room with a single K5.6 QR Head @ .18 over 1500 Ft2. His reasoning is that the tank is not combustible, just the product in it ....... Im leaning towards a EH designation in the event of fire the fuel would be more than capable of supporting combustion. At the very least I dont see the current configuration as being adequate. Thanks, Dave P. An AHJ in NJ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)