OH2 sounds good to me. As long as the total amount of Class II in the
room is less than the maximum allowable quantity per IFC the use of the
room remains classified the same as the rest of the building. I believe
the MAQ is 660 gallons before the occupancy would change to "H"
requiring extra hazard sprinkler system.

Ron Fletcher
Aero Automatic
Phoenix, AZ 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David
Phelan
Sent: Monday, March 10, 2008 10:51 AM
To: [email protected]
Subject: Fuel Tank Rooms

How does the group feel on the occupancy classification of a rated room
in a building that contains a 275 Gal #2 Fuel tank for the rooftop
generator?  The room is on the ground level and the tank is 130 feet
above on the roof.
   
  The architect is calling this a OH2 hazard and protecting the room
with a single K5.6 QR Head @ .18 over 1500 Ft2.  His reasoning is that
the tank is not combustible, just the product in it .......  Im leaning
towards a EH designation in the event of fire the fuel would be more
than capable of supporting combustion.  At the very least I dont see the
current configuration as being adequate.
   
  Thanks,
   
  Dave P.
  An AHJ in NJ
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to