How big is the room?

At 01:51 PM 3/10/2008, you wrote:
How does the group feel on the occupancy classification of a rated room in a building that contains a 275 Gal #2 Fuel tank for the rooftop generator? The room is on the ground level and the tank is 130 feet above on the roof.

The architect is calling this a OH2 hazard and protecting the room with a single K5.6 QR Head @ .18 over 1500 Ft2. His reasoning is that the tank is not combustible, just the product in it ....... Im leaning towards a EH designation in the event of fire the fuel would be more than capable of supporting combustion. At the very least I dont see the current configuration as being adequate.

  Thanks,

  Dave P.