How big is the room?
At 01:51 PM 3/10/2008, you wrote:
How does the group feel on the occupancy classification of a rated
room in a building that contains a 275 Gal #2 Fuel tank for the
rooftop generator? The room is on the ground level and the tank is
130 feet above on the roof.
The architect is calling this a OH2 hazard and protecting the
room with a single K5.6 QR Head @ .18 over 1500 Ft2. His reasoning
is that the tank is not combustible, just the product in it
....... Im leaning towards a EH designation in the event of fire
the fuel would be more than capable of supporting combustion. At
the very least I dont see the current configuration as being adequate.
Thanks,
Dave P.
An AHJ in NJ