That makes no sense.  Of course the valve room is the responsibility of
the A/E, not the sprinkler contractor.  If the area isn't heated and
there is a riser there then as the FP contractor you'd let the GC know
of the issue.  The FP contractor shouldn't be held responsible for
building rooms or buildings.  


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
Sent: Thursday, March 13, 2008 1:52 PM
To: [email protected]
Subject: Re: Dry System Size

If this building were to have a cafeteria/kitchen but no space was
provided for the cooking line would it be the responsibility of the
appliance supplier to "find" a location for it or would it be an
oversight of the A&E?
Did the A&E not know that there was going to be a sprinkler system? If
not there seems to be some negligence. If so isn't it the A&E to provide
a location? I bet they have a telephone room. I bet they have....

On 3/13/08, [EMAIL PROTECTED] <[EMAIL PROTECTED]> wrote:
>
> Doesn't specifically say you HAVE to have one but in order to provide 
> heat for a dry valve in an open space it's the only choice.  NFPA 13, 
> 2007, 7.2.5.2
>
>
> Craig L. Prahl, CET
> Fire Protection Group
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax - 
> 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
>
> [mailto:[EMAIL PROTECTED] On Behalf Of Roland 
> Huggins
> Sent: Thursday, March 13, 2008 1:16 PM
> To: [email protected]
>
> Subject: Re: Dry System Size
>
> Here's an interesting twist on this issue.  Where does it say that you

> have to have a valve room?
>
> Roland
>
> On Mar 13, 2008, at 10:06 AM, Thom McMahon wrote:
>
> > I have seen the RPZ and dry valves under the first landing of the 
> > stairs, then this area is enclosed and heated. Remember your riser 
> > is wet and subject to freezing below the clapper of the DPV. Due to 
> > the low overhead and access issue's this arrangement would require 
> > AHJ approval, if the 1st landing is less than 7'-0" AFF.
> >
> > Thom McMahon
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to