You do not need a valve room.  The valve must be maintained above
freezing is the only requirement as far as temperature is concerned.

John

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES 


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, March 13, 2008 1:27 PM
To: [email protected]
Subject: RE: Dry System Size

Doesn't specifically say you HAVE to have one but in order to provide
heat for a dry valve in an open space it's the only choice.  NFPA 13,
2007, 7.2.5.2 


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, March 13, 2008 1:16 PM
To: [email protected]
Subject: Re: Dry System Size

Here's an interesting twist on this issue.  Where does it say that you
have to have a valve room?

Roland

On Mar 13, 2008, at 10:06 AM, Thom McMahon wrote:

> I have seen the RPZ and dry valves under the first landing of the 
> stairs, then this area is enclosed and heated. Remember your riser is 
> wet and subject to freezing below the clapper of the DPV. Due to the 
> low overhead and access issue's this arrangement would require AHJ 
> approval, if the 1st landing is less than 7'-0" AFF.
>
> Thom McMahon

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to