Tell those crazy europeans that ;-), about the inward swinging doors!!
Mark at Aero

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, March 25, 2008 6:55 AM
To: [email protected]
Subject: Re: fire pump room doors


Greg,

Egress doors only have to open in the direction of egress if the 
calculated occupancy load is 50 or more persons or the occupancy is Group 
H. See 1008.1.2.  I don't recall the last time I saw inward swinging 
doors.

I hope this helps.

James L.(Jim) Roberts, PE/SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)





"Greg McGahan" <[EMAIL PROTECTED]>
Sent by:  [EMAIL PROTECTED]
03/25/2008 08:09 AM
Please respond to sprinklerforum

To
<[email protected]>
cc

Subject
fire pump room doors







I do not have access to the current edition of the IBC this morning and I 
do
not see it in NFPA 20.... Is there a requirement that fire pump rooms have
doors exiting to the exterior of a building?

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to