Joe, Thanks for the insight. My concern is a situation where a client has a Chapter 13 (2007) rack storage arrangement and wants to establish a "safe zone" between the rack storage and adjacent combustibles. The client wants to be able to say at "X" distance the target will not be ignited prior to sprinkler control of the rack fire.
Any feel for the value of "X", again assuming Chap 13 stg? Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146 410-544-3620 Phone 410-544-3032 FAX 412-400-6528 Cell -------- Original Message -------- Subject: Re: Aisle Width for Misc Storage From: Joe Hankins <[EMAIL PROTECTED]> Date: Mon, March 31, 2008 10:18 am To: [email protected] Bill, It does not mean no aisle jump. In the tests that Class I-IV protection are based on, a test was considered successful even if ignition occurred across the aisle but was contained (did not burn through to the other side) of the target rack. Joe [EMAIL PROTECTED] wrote: > What is the minimum aisle width in order to use the ceiling only > densities for miscellaneous rack storage (Chap 13 - 2007)? Aisle widths > are specified in Chapter 16 but not in Chapter 13. Would this width be > 3.5 ft per 3.9.3.7.5? > > I'm assuming this would mean there's no ignition across a 3.5 ft aisle > if Table 13.2.1 is applied. > > Bill Brooks > > William N. Brooks, P.E. > Brooks Fire Protection Engineering Inc. > 372 Wilett Drive > Severna Park, MD 21146 > 410-544-3620 Phone > 410-544-3032 FAX > 412-400-6528 Cell > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)