I would start with the criteria on adjacent hazards. Seems that
tells you everything you need to know.
Roland
On Mar 31, 2008, at 7:38 AM, [EMAIL PROTECTED] wrote:
Joe,
Thanks for the insight. My concern is a situation where a client
has a
Chapter 13 (2007) rack storage arrangement and wants to establish a
"safe zone" between the rack storage and adjacent combustibles. The
client wants to be able to say at "X" distance the target will not be
ignited prior to sprinkler control of the rack fire.
Any feel for the value of "X", again assuming Chap 13 stg?
Bill Brooks
William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell
-------- Original Message --------
Subject: Re: Aisle Width for Misc Storage
From: Joe Hankins <[EMAIL PROTECTED]>
Date: Mon, March 31, 2008 10:18 am
To: [email protected]
Bill,
It does not mean no aisle jump. In the tests that Class I-IV
protection
are based on, a test was considered successful even if ignition
occurred
across the aisle but was contained (did not burn through to the other
side) of the target rack.
Joe
[EMAIL PROTECTED] wrote:
What is the minimum aisle width in order to use the ceiling only
densities for miscellaneous rack storage (Chap 13 - 2007)? Aisle
widths
are specified in Chapter 16 but not in Chapter 13. Would this
width be
3.5 ft per 3.9.3.7.5?
I'm assuming this would mean there's no ignition across a 3.5 ft
aisle
if Table 13.2.1 is applied.
Bill Brooks
William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)