I'm fighting somewhat the same battle with a
local community. But here the FM said over the
phone that the water company doesn't allow
connection to a 3/4" line. However, his letter
said that 3/4" will not work, even though the
calcs show that it will. I'll be interested in others experience.
At 12:38 AM 4/2/2008, you wrote:
From: McCormick, Mark <[EMAIL PROTECTED]>
To: Los Angeles Area Fire Marshals Association <[EMAIL PROTECTED]>
Sent: Tue Apr 01 21:48:50 2008
Subject: [laafma] Pipe Velocity in 3/4" Water Service Lateral
We adopted a sprinkler ordinance in January for SFDs and now are dealing
with some of the vacant lots in town that have a ¾ copper water service
lateral with a 1 meter.
Our Water Department (regulates from the corporation stop to the customer
side of the meter) has a maximum velocity standard of 15 feet per second.
When you flow 26 gpm through a ¾ inch service lateral the velocity is in the
30 fps range.
I am proposing we stay with NFPA 13D, the guiding design standard for
residential sprinklers in SFDs. 13D does not seem to have a velocity
requirement and does allow ¾ pipe as long as hydraulically the pressure and
flow is available.
New subdivisions will have a 1.5 lateral so we wont have the problem in
the future.
Has anyone ran into the velocity issue for residential 13D systems?
If so, were you successful in getting around the hurdle?
We do not believe exceeding the velocity in ¾ copper for a test and
possible fire will be an issue.
Thanks for any information you have.
Mark
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)