It should be EMPHATICALLY noted to the water purveyor that this NOT 
"continuous" flow, only "intermittent" flow (terms of their trade".  There is 
no reasonable basis for denying the arrangemaent you describe for a life afety 
system that will hopefully never operate at full flow rate in its lifespan. 


Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: Joe Hankins <[EMAIL PROTECTED]>

Date: Wed, 02 Apr 2008 09:14:35 
To:[email protected]
Subject: Re: Pipe Velocity in 3/4" water service lateral


There is nothing inherently wrong with a 30 ft/sec velocity in pipe. The 
higher the velocity, the higher the friction loss, but if you can get 
the needed flow and pressure, that's all that matters. There have been 
claims floating around for years that friction loss calculations are 
inaccurate when the velocity is high, but that is not true. In the past, 
some manufacturers of check valves and water meters put a 32 ft/sec 
limit on flows through their devices, but that was to prevent damage.

Factory Mutual had a design velocity limit for small branch line piping 
in grids, but that was done in an attempt to prevent silly designs (e.g. 
300 ft. long 1 inch branch lines) that saved a few pennies but the 
system could not tolerate even one extra head operating on a branch 
line. That created so much confusion (people were being told to replace 
piping in existing systems that had high velocity because they wouldn't 
control a fire!) that the limit was eliminated.

I actually heard someone explain the velocity limit by saying that the 
water couldn't "make the turn" to flow out of an open sprinkler and 
would just flow past it!

Joe

Mark Pedroia wrote:
> From: McCormick, Mark <[EMAIL PROTECTED]>
> To: Los Angeles Area Fire Marshals Association <[EMAIL PROTECTED]>
> Sent: Tue Apr 01 21:48:50 2008
> Subject: [laafma] Pipe Velocity in 3/4" Water Service Lateral
>
> We adopted a sprinkler ordinance in January for SFD’s and now are dealing
> with some of the vacant lots in town that have a ¾” copper water service
> lateral with a 1” meter.
>
> Our Water Department (regulates from the corporation stop to the customer
> side of the meter) has a maximum velocity standard of 15 feet per second.
> When you flow 26 gpm through a ¾ inch service lateral the velocity is in the
> 30 fps range.
>
> I am proposing we stay with NFPA 13D, the guiding design standard for
> residential sprinklers in SFD’s. 13D does not seem to have a velocity
> requirement and does allow ¾” pipe as long as hydraulically the pressure and
> flow is available.
>
> New subdivisions will have a 1.5” lateral so we won’t have the problem in
> the future.
>
> Has anyone ran into the velocity issue for residential 13D systems?
>
> If so, were you successful in getting around the hurdle?
>
> We do not believe exceeding the velocity in ¾” copper for a test and
> possible fire will be an issue.
>
> Thanks for any information you have.
>
> Mark
>
>  
>
>_______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>   

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to