>From what I've been taught the higher the velocities the less accurate the
hydraulic calculations are but it is a 'self correcting' scenario since if
you have pipes w/ say 40 fps velocities your friction loss will be SKY HIGH
and you will have to upsize the pipe accordingly. NFPA has no velocity
limitations so I don't know where AHJ's get this info from - and we do have
a few here locally that impose 32 fps.

I've done a ton of residential work w/ a 3/4" feed from city main to 1"
water meter. Usually if the run is over 15' you're losing MOST of your
friction loss in that single piece of pipe. If there is high enough pressure
it can still work but now that people are becoming more accustomed to fire
sprinklers, here locally, they're putting in 1" yokes in all new lots.

A fire inspector once, very assertively, told me that smaller pipe increases
pressure. I kinda chuckled and tried to explain it increases velocities but
the only way you're increasing pressure is with a booster pump or gravity.




On 4/2/08, Thom McMahon <[EMAIL PROTECTED]> wrote:
>
> Generally I think all limits on velocity are related to the plumbing code,
> which has a 10fps limit. The reason is that above that there is a distinct
> noise associated with flows over 15 fps. While noise is an issue, in a fire
> situation, with the smoke detector going off, the sprinkler head flowing
> like a freight train, and everyone scrambling for the door, I don't see
> noise as very  important. Exceeding a "Policy" velocity in an emergency such
> as fire is a no brainer. Fire Departments do it all the time.
>
> Thom McMahon
> Firetech, Inc.
> 2560 Copper Ridge Dr
> Steamboat Springs, CO 80488-2136
> Tel: 970-879-7952
> Fax: 970-879-7926
> ----- Original Message ----- From: "Joe Hankins" <[EMAIL PROTECTED]>
> To: <[email protected]>
> Sent: Wednesday, April 02, 2008 7:14 AM
> Subject: Re: Pipe Velocity in 3/4" water service lateral
>
>
> There is nothing inherently wrong with a 30 ft/sec velocity in pipe. The
> higher the velocity, the higher the friction loss, but if you can get
> the needed flow and pressure, that's all that matters. There have been
> claims floating around for years that friction loss calculations are
> inaccurate when the velocity is high, but that is not true. In the past,
> some manufacturers of check valves and water meters put a 32 ft/sec
> limit on flows through their devices, but that was to prevent damage.
>
> Factory Mutual had a design velocity limit for small branch line piping
> in grids, but that was done in an attempt to prevent silly designs (e.g.
> 300 ft. long 1 inch branch lines) that saved a few pennies but the
> system could not tolerate even one extra head operating on a branch
> line. That created so much confusion (people were being told to replace
> piping in existing systems that had high velocity because they wouldn't
> control a fire!) that the limit was eliminated.
>
> I actually heard someone explain the velocity limit by saying that the
> water couldn't "make the turn" to flow out of an open sprinkler and
> would just flow past it!
>
> Joe
>
> Mark Pedroia wrote:
>
> > From: McCormick, Mark <[EMAIL PROTECTED]>
> > To: Los Angeles Area Fire Marshals Association <[EMAIL PROTECTED]>
> > Sent: Tue Apr 01 21:48:50 2008
> > Subject: [laafma] Pipe Velocity in 3/4" Water Service Lateral
> >
> > We adopted a sprinkler ordinance in January for SFD's and now are
> > dealing
> > with some of the vacant lots in town that have a ¾" copper water service
> > lateral with a 1" meter.
> >
> > Our Water Department (regulates from the corporation stop to the
> > customer
> > side of the meter) has a maximum velocity standard of 15 feet per
> > second.
> > When you flow 26 gpm through a ¾ inch service lateral the velocity is in
> > the
> > 30 fps range.
> >
> > I am proposing we stay with NFPA 13D, the guiding design standard for
> > residential sprinklers in SFD's. 13D does not seem to have a velocity
> > requirement and does allow ¾" pipe as long as hydraulically the pressure
> > and
> > flow is available.
> >
> > New subdivisions will have a 1.5" lateral so we won't have the problem
> > in
> > the future.
> >
> > Has anyone ran into the velocity issue for residential 13D systems?
> >
> > If so, were you successful in getting around the hurdle?
> >
> > We do not believe exceeding the velocity in ¾" copper for a test and
> > possible fire will be an issue.
> >
> > Thanks for any information you have.
> >
> > Mark
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> > (Put the word unsubscribe in the subject field)
> >
> >
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> (Put the word unsubscribe in the subject field)
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to