When I "look up" at work that is incorrect, I always wonder if there was
an engineer of record involved on the project. Then I wonder how much
money they were paid to be the "engineer of record."  Then I wonder how
much time they actually spent on their "performance spec" that included
no performance criteria outside of references to code.

Obviously, mine is a cynical perspective of my colleagues in the
engineering world.  I certainly understand the reality that there aren't
enough skilled engineers to be involved on all sprinkler projects. To
say the typical "performance spec" is criminal may be excessive (maybe
they couldn't get enough fee to do the project justice...?) But I do
know that all engineers who rely on their blanket statement about
systems "meeting code" (but don't have the ability to verify compliance)
to are teed-up nicely to lose the litigation battle should a fire ever
occur. As Chris has reminded us, there seem to be an inordinate number
of screwed up systems out there, so it's really a wonder why more
engineers aren't brought to task through litigation.  Sometime I wonder
if it is because of the ironic fact that "everyone" knows the mechanical
engineer is not the expert - it's the sprinkler contractor.  So
engineers are forgotten when problems arise...???

Don't mean to tangent into another PE-bashing thread, but it just peeves
me that there are "professionals" getting paid for being lazy fools.

Mark A. Sornsin, PE 
Fire Protection Engineer 
Ulteig Engineers, Inc. 
Fargo, ND  
701.280.8591
[EMAIL PROTECTED] 
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Cahill
Sent: Wednesday, April 02, 2008 12:29 PM
To: [email protected]
Subject: Do you look up?

I imagine, like me, you all (ya'll for some of you) on the very rare
occasions you are not working look around at sprinkler systems where you
live, shop and play. 

 

It's a very rare occasion I don't see something that appears deficient.
For
example, in a grocery store the one head on the back side of the main is
missing over HPS and a mess of piping creating a ceiling without heads
under
them, at a Home Depot 190 psi on the wet side of an auxiliary dry valve,
or
the local high school with sidewall heads about 15-20' down from the
peak of
the very large skylight.  This is all in the last two days as an example
but
see similar all the time.  

 

The sad part is I'm not really trying.  What if I had the plans and
calcs,
how much more would there be?  Or really looked at the whole building
instead of a casual look at where I happen to be?  Or the scary part
what if
I actually considered the hazard vs. the design?  

 

I also realize two issues - most times what I see probably won't cause
the
system to fail in a fire IF that is the only thing wrong.  There is a
"probably" and an "if " in the last sentence which means there are cases
that will fail, just not many IMHO.   And second we make mistakes too.  

 

The heads at the peak - just because an AHJ didn't call it a deficiency
doesn't mean it's OK.  Certainly it is possible there is a documented
and
proactively approved alternate method out there on this but I strongly
doubt
it.  Now I'm sure the missing head has a perfectly rational explanation
of
how it got like that.  The W.O. is there and it must be plugged or the
system is off.  It's not a TI thing long after the original
construction;
this is a very new building.  Can't rationalize how you get 190 psi by
accident or approval.  

 

MN is more regulated than most (but not all) areas.  Do you see this
stuff
too?  What if anything can you really do about it?         

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: [EMAIL PROTECTED]

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to