What kind of variance in calcs from actual bucket test results are
considered acceptable? I'm just curious since taking out the head and
flowing straight from a 1/2" threaded outlet vs. flowing a 7/16" orifice
(like a 4.2k sprinkler w/ element removed) could possibly work in your favor
to a small degree but could also work against you depending on what k-factor
of sprinkler you used.


In a 13R bucket test do you actually remove more than one sprinkler and flow
up to four? Or is it always just one? Seems like a source calc w/ one
sprinkler flowing would make more sense if you're only required to bucket
test one sprinkler...

-B-




On 4/9/08, Todd Williams - FPDC <[EMAIL PROTECTED]> wrote:
>
> If you have a really bad water supply, instead of a pitot you use a
> 5-gallon bucket and a stop watch. 8-)
>
>
> At 02:19 PM 4/9/2008, you wrote:
>
> > This is the first time I've heard it being done for 13R. 13D, yes. But
> > not
> > 13R. Are there other jurisdictions requiring a bucket test for 13R?
> >
> > Tony
> >
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] On Behalf Of Brian
> > Harris
> > Sent: April 9, 2008 12:01 PM
> > To: [email protected]
> > Subject: RE: What is a Bucket Test?
> >
> > A bucket test / barrel test is when you remove a head(s) in the remote
> > area
> > and fill up a bucket/barrel to see if it is flowing the gpm the is
> > called
> > for in the calc's. In our case with the density and heads we are using
> > that
> > would be 20 gpm, we are getting around 15 gpm.
> >
> >
> > Brian Harris
> > FDFP INC.
> >
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] On Behalf Of
> > [EMAIL PROTECTED]
> > Sent: Wednesday, April 09, 2008 1:50 PM
> > To: [email protected]
> > Subject: What is a Bucket Test?
> >
> > Perhaps a dumb question, but what is a bucket test and is it conducted
> > the
> > same way in every jurisdiction?
> >
> > Bill Brooks
> >
> > William N. Brooks, P.E.
> > Brooks Fire Protection Engineering Inc.
> > 372 Wilett Drive
> > Severna Park, MD 21146
> > 410-544-3620 Phone
> > 410-544-3032 FAX
> > 412-400-6528 Cell
> >
> > -------- Original Message --------
> > Subject: Failed Bucket Test
> > From: "Brian Harris" <[EMAIL PROTECTED]>
> > Date: Mon, April 07, 2008 2:30 pm
> > To: <[email protected]>
> >
> > Fellow forum people:
> > I have a situation where we have designed and installed a 13R system, it
> > is
> > completely finished and wham-o we fail the bucket test! Our system was
> > designed based on the flow test provided by the city fire dept., turns
> > out
> > that a test taken now with the failed test shows a 25% drop in static &
> > residual pressures, hence the failed test. Of course the owner is
> > looking to
> > us to pull a magic rabbit out of our #$% , err I mean hat, we have tried
> > a
> > few different things but with that big of a pressure loss there's really
> > not
> > much we can do. I don't feel it's our liability at this point since we
> > went
> > off the city's water flow test and per the calc's we were good, any
> > thoughts?
> >
> >
> > Regards,
> >
> >
> > <http://www.firstdefensefire.com/>
> >
> >
> >
> >
> >
> >
> >
> >
> > E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
> > 5.09560 http://www.pctools.com/spyware-doctor/
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> > (Put the word unsubscribe in the subject field)
> >
> >
> >
> >
> >
> > E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
> > 5.09590 http://www.pctools.com/spyware-doctor/
> >
> >
> >
> >
> >
> > E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
> > 5.09590 http://www.pctools.com/spyware-doctor/
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> > (Put the word unsubscribe in the subject field)
> >
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080  _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>