So, you start with the system dry, then open the valve?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

-------- Original Message --------
Subject: RE: What is a Bucket Test?
From: "A.P.Silva" <[EMAIL PROTECTED]>
Date: Wed, April 09, 2008 6:17 pm
To: [email protected]

It should be same orifice as head. Also same number of heads as in
design.
What will a single 1/2" outlet tell you when you have 4, 7/16" outlets
in
your design area.

At the time bucket tests were starting to be done, residential heads had
two
flow requirements. One for single head and another for multiple heads.
So
for 13D systems the bucket test was done with a single head flowing and
also
for two heads flowing simultaneously. An actual head with the guts
broken
was used at the outlet. At least this is how it is done in my area.

Tony

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of IPA
Sent: April 9, 2008 1:47 PM
To: [email protected]
Subject: Re: What is a Bucket Test?

What kind of variance in calcs from actual bucket test results are
considered acceptable? I'm just curious since taking out the head and
flowing straight from a 1/2" threaded outlet vs. flowing a 7/16" orifice
(like a 4.2k sprinkler w/ element removed) could possibly work in your
favor
to a small degree but could also work against you depending on what
k-factor
of sprinkler you used.


In a 13R bucket test do you actually remove more than one sprinkler and
flow
up to four? Or is it always just one? Seems like a source calc w/ one
sprinkler flowing would make more sense if you're only required to
bucket
test one sprinkler...

-B-




On 4/9/08, Todd Williams - FPDC <[EMAIL PROTECTED]> wrote:
>
> If you have a really bad water supply, instead of a pitot you use a
> 5-gallon bucket and a stop watch. 8-)
>
>
> At 02:19 PM 4/9/2008, you wrote:
>
> > This is the first time I've heard it being done for 13R. 13D, yes.
> > But not 13R. Are there other jurisdictions requiring a bucket test
> > for 13R?
> >
> > Tony
> >
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] On Behalf Of Brian
> > Harris
> > Sent: April 9, 2008 12:01 PM
> > To: [email protected]
> > Subject: RE: What is a Bucket Test?
> >
> > A bucket test / barrel test is when you remove a head(s) in the
> > remote area and fill up a bucket/barrel to see if it is flowing the
> > gpm the is called for in the calc's. In our case with the density
> > and heads we are using that would be 20 gpm, we are getting around
> > 15 gpm.
> >
> >
> > Brian Harris
> > FDFP INC.
> >
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] On Behalf Of
> > [EMAIL PROTECTED]
> > Sent: Wednesday, April 09, 2008 1:50 PM
> > To: [email protected]
> > Subject: What is a Bucket Test?
> >
> > Perhaps a dumb question, but what is a bucket test and is it conducted
> > the
> > same way in every jurisdiction?
> >
> > Bill Brooks
> >
> > William N. Brooks, P.E.
> > Brooks Fire Protection Engineering Inc.
> > 372 Wilett Drive
> > Severna Park, MD 21146
> > 410-544-3620 Phone
> > 410-544-3032 FAX
> > 412-400-6528 Cell
> >
> > -------- Original Message --------
> > Subject: Failed Bucket Test
> > From: "Brian Harris" <[EMAIL PROTECTED]>
> > Date: Mon, April 07, 2008 2:30 pm
> > To: <[email protected]>
> >
> > Fellow forum people:
> > I have a situation where we have designed and installed a 13R system, it
> > is
> > completely finished and wham-o we fail the bucket test! Our system was
> > designed based on the flow test provided by the city fire dept., turns
> > out
> > that a test taken now with the failed test shows a 25% drop in static &
> > residual pressures, hence the failed test. Of course the owner is
> > looking to
> > us to pull a magic rabbit out of our #$% , err I mean hat, we have tried
> > a
> > few different things but with that big of a pressure loss there's really
> > not
> > much we can do. I don't feel it's our liability at this point since we
> > went
> > off the city's water flow test and per the calc's we were good, any
> > thoughts?
> >
> >
> > Regards,
> >
> >
> > <http://www.firstdefensefire.com/>
> >
> >
> >
> >
> >
> >
> >
> >
> > E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
> > 5.09560 http://www.pctools.com/spyware-doctor/
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> >
to:[EMAIL PROTECTED]<[EMAIL PROTECTED]
sprinkler.org>
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> >
to:[EMAIL PROTECTED]<[EMAIL PROTECTED]
sprinkler.org>
> > (Put the word unsubscribe in the subject field)
> >
> >
> >
> >
> >
> > E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
> > 5.09590 http://www.pctools.com/spyware-doctor/
> >
> >
> >
> >
> >
> > E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
> > 5.09590 http://www.pctools.com/spyware-doctor/
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> >
to:[EMAIL PROTECTED]<[EMAIL PROTECTED]
sprinkler.org>
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> >
to:[EMAIL PROTECTED]<[EMAIL PROTECTED]
sprinkler.org>
> > (Put the word unsubscribe in the subject field)
> >
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080 _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]<[EMAIL PROTECTED]
sprinkler.org>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to