This whole bucket thing sounds asinine to me... I mean, obviously Brian has
a problem here with the water supply but the bucket test in general doesn't
sound real
practical. Anyone could've looked at the guage and realized their
was a problem without a bunch of people sitting around holding
buckets under open heads. Hydraulic calculations are theoretical in
nature...
This especially doesn't make much sense if ahj's are requiring this for 13d
systems which
can be calculated based upon a static pressure only....




On 4/9/08, A.P.Silva <[EMAIL PROTECTED]> wrote:
>
> The system is wet. You make up an assembly that will include a valve and
> orifice. The sprinkler head/s at the test location removed and substituted
> with the assembly. The valve at the outlet is opened and water collected
> in
> a bucket. In essence the test is a verification of the design calculations
> and installation. And I guess the water supply.
>
>
> Tony
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of
>
> [EMAIL PROTECTED]
> Sent: April 9, 2008 5:58 PM
> To: [email protected]
> Subject: RE: What is a Bucket Test?
>
> So, you start with the system dry, then open the valve?
>
> Bill Brooks
>
> William N. Brooks, P.E.
> Brooks Fire Protection Engineering Inc.
> 372 Wilett Drive
> Severna Park, MD 21146
> 410-544-3620 Phone
> 410-544-3032 FAX
> 412-400-6528 Cell
>
> -------- Original Message --------
> Subject: RE: What is a Bucket Test?
> From: "A.P.Silva" <[EMAIL PROTECTED]>
> Date: Wed, April 09, 2008 6:17 pm
> To: [email protected]
>
> It should be same orifice as head. Also same number of heads as in design.
> What will a single 1/2" outlet tell you when you have 4, 7/16" outlets in
> your design area.
>
> At the time bucket tests were starting to be done, residential heads had
> two
> flow requirements. One for single head and another for multiple heads.
> So
> for 13D systems the bucket test was done with a single head flowing and
> also
> for two heads flowing simultaneously. An actual head with the guts broken
> was used at the outlet. At least this is how it is done in my area.
>
> Tony
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of IPA
> Sent: April 9, 2008 1:47 PM
> To: [email protected]
> Subject: Re: What is a Bucket Test?
>
> What kind of variance in calcs from actual bucket test results are
> considered acceptable? I'm just curious since taking out the head and
> flowing straight from a 1/2" threaded outlet vs. flowing a 7/16" orifice
> (like a 4.2k sprinkler w/ element removed) could possibly work in your
> favor
> to a small degree but could also work against you depending on what
> k-factor
> of sprinkler you used.
>
>
> In a 13R bucket test do you actually remove more than one sprinkler and
> flow
> up to four? Or is it always just one? Seems like a source calc w/ one
> sprinkler flowing would make more sense if you're only required to bucket
> test one sprinkler...
>
> -B-
>
>
>
>
> On 4/9/08, Todd Williams - FPDC <[EMAIL PROTECTED]> wrote:
> >
> > If you have a really bad water supply, instead of a pitot you use a
> > 5-gallon bucket and a stop watch. 8-)
> >
> >
> > At 02:19 PM 4/9/2008, you wrote:
> >
> > > This is the first time I've heard it being done for 13R. 13D, yes.
> > > But not 13R. Are there other jurisdictions requiring a bucket test
> > > for 13R?
> > >
> > > Tony
> > >
> > > -----Original Message-----
> > > From: [EMAIL PROTECTED]
> > > [mailto:[EMAIL PROTECTED] On Behalf Of Brian
> > > Harris
> > > Sent: April 9, 2008 12:01 PM
> > > To: [email protected]
> > > Subject: RE: What is a Bucket Test?
> > >
> > > A bucket test / barrel test is when you remove a head(s) in the
> > > remote area and fill up a bucket/barrel to see if it is flowing the
> > > gpm the is called for in the calc's. In our case with the density
> > > and heads we are using that would be 20 gpm, we are getting around
> > > 15 gpm.
> > >
> > >
> > > Brian Harris
> > > FDFP INC.
> > >
> > > -----Original Message-----
> > > From: [EMAIL PROTECTED]
> > > [mailto:[EMAIL PROTECTED] On Behalf Of
> > > [EMAIL PROTECTED]
> > > Sent: Wednesday, April 09, 2008 1:50 PM
> > > To: [email protected]
> > > Subject: What is a Bucket Test?
> > >
> > > Perhaps a dumb question, but what is a bucket test and is it
> > > conducted the same way in every jurisdiction?
> > >
> > > Bill Brooks
> > >
> > > William N. Brooks, P.E.
> > > Brooks Fire Protection Engineering Inc.
> > > 372 Wilett Drive
> > > Severna Park, MD 21146
> > > 410-544-3620 Phone
> > > 410-544-3032 FAX
> > > 412-400-6528 Cell
> > >
> > > -------- Original Message --------
> > > Subject: Failed Bucket Test
> > > From: "Brian Harris" <[EMAIL PROTECTED]>
> > > Date: Mon, April 07, 2008 2:30 pm
> > > To: <[email protected]>
> > >
> > > Fellow forum people:
> > > I have a situation where we have designed and installed a 13R
> > > system, it is completely finished and wham-o we fail the bucket
> > > test! Our system was designed based on the flow test provided by the
> > > city fire dept., turns out that a test taken now with the failed
> > > test shows a 25% drop in static & residual pressures, hence the
> > > failed test. Of course the owner is looking to us to pull a magic
> > > rabbit out of our #$% , err I mean hat, we have tried a few
> > > different things but with that big of a pressure loss there's really
> > > not much we can do. I don't feel it's our liability at this point
> > > since we went off the city's water flow test and per the calc's we
> > > were good, any thoughts?
> > >
> > >
> > > Regards,
> > >
> > >
> > > <http://www.firstdefensefire.com/>
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > > E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
> > > 5.09560 http://www.pctools.com/spyware-doctor/
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email
> > >
> to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> <[EMAIL PROTECTED]
> sprinkler.org>
> > > (Put the word unsubscribe in the subject field)
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email
> > >
> to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> <[EMAIL PROTECTED]
> sprinkler.org>
> > > (Put the word unsubscribe in the subject field)
> > >
> > >
> > >
> > >
> > >
> > > E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
> > > 5.09590 http://www.pctools.com/spyware-doctor/
> > >
> > >
> > >
> > >
> > >
> > > E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
> > > 5.09590 http://www.pctools.com/spyware-doctor/
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email
> > >
> to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> <[EMAIL PROTECTED]
> sprinkler.org>
> > > (Put the word unsubscribe in the subject field)
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email
> > >
> to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> <[EMAIL PROTECTED]
> sprinkler.org>
> > > (Put the word unsubscribe in the subject field)
> > >
> >
> > Todd G. Williams, PE
> > Fire Protection Design/Consulting
> > Stonington, Connecticut
> > www.fpdc.com
> > 860.535.2080 _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> <[EMAIL PROTECTED]
> sprinkler.org>
> > (Put the word unsubscribe in the subject field)
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> (Put the word unsubscribe in the subject field)
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to