Ron,
NFPA 13 (2002) sect. 7.2.3.4 states "Check valves shall not be used
to subdivide the dry pipe system." To me, that says that check valves
cannot be used for any purpose on a dry system since they will, by
their nature, subdivide a system. Since a check valve is now required
on floor controls, you can probably not install a "floor control" on
a dry system. You could install an isolation valve on each floor and
that is about it. (note to thread readers: I did not look up the
specific wording of the 13 section until I prepared this post)
Todd
Todd, although you can't use check valves to segregate sections of the
system you have to have the check valves. Two separate requirements.
One has to do with isolating the floor for service. The other has to
do with water delivery time.
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com