Eric,

True, but as long as we're in a code/standard interpretation exercise
14 requires the check valve on combined systems. My guess on this is
that the anticipated combined systems would all be manual or automatic
wet but 14 doesn't apply this restriction so for the purpose of our
exercise the dry combined system is allowed subject to all the
restrictions in 14. I'm trying real hard here to keep the
code/standard analyst hat on for this whole thing and avoid the "is it
a good idea" question.

On Thu, Apr 10, 2008 at 10:32 AM, Eric Tysinger <[EMAIL PROTECTED]> wrote:
> Good afternoon gentlemen,
>
>  Just a thought on this. In my opinion only, the use of the check valve
>  by itself constitutes sub-divison of the system. However, once you
>  create separate floor controls, that in itself creates the
>  sub-divisions. The addition of the check valve (due to the floor control
>  requitements of NFPA) would not be for the purpose of sub-division.
>
>  On the other hand, the purpose of the check valve with the floor control
>  is to trap water and pressure on the system side of a particular floor
>  to provide some protection on the floor while other portions of the
>  system are down for maintenance. With dry systems there is nothing on
>  the system side except for possibly air or what have you. The check
>  valve in that case would be usless.
>
>  Eric Tysinger
>  Design Manager
>  Wayne Automatic Fire Sprinklers, Inc.
>
>
>
>
>
>  -----Original Message-----
>  From: [EMAIL PROTECTED]
>  [mailto:[EMAIL PROTECTED] On Behalf Of Ron
>  Greenman
>  Sent: Thursday, April 10, 2008 12:27 PM
>  To: [email protected]
>  Subject: Re: Check valves and dry systems
>
>  Todd,
>
>  That was what I was talking about in my last post. You cannot subdivide
>  the dry piper with check valves. One reason I can think of is because
>  when new and they work you have one water delivery time but as they age
>  and leak each subdivision that does so adds time to decompression and so
>  to water delivery also. I've seen this problem and so from this
>  standpoint this recent (maybe 99) in 13 makes sense.
>  The other problem I can imagine is the clapper on a swing check
>  "glueing" itself shut due to disuse.On the one's I'm familiar with that
>  was never a problem.
>
>  Back to subdivision. 13 does not (and I admit I'm stretching this and
>  remember that I don't like the idea but I'm not the owner, designer,
>  layout tech or the AHJ and am merely arguing code/standard points)
>  prohibit check valves in dry systems. It specifically prohibits using
>  them for subdivision. Again, if water delivery time was what prompted
>  the prohibition, then testing the system with the check valves removed
>  and replaced by spools effectively addresses the prohibition since the
>  now missing clappers are not there to hold air back and so you are
>  getting a realistic picture of the entire system rather than just the
>  riser and one floor.
>
>  Would IU recommend such a scheme. Never, but not because the schema
>  itself is without logical merit but rather because of the ridiculous
>  costs and the tendency to "cheat" associated with IT&M.
>
>  Part of the argument here revolves around committee intent. Why is this
>  rule there in the first place (like the 52K square footage limitation)?
>  Is it there because it's always been there and we don't remember why
>  (Like 52K)? Is it there because a problem was discovered and this is a
>  fix (maybe like this prohibition against subdivision by check valve in
>  dry pipes)? Is it there because some vendor has come out with a new
>  product that meets a need and rules for its use are needed (the section
>  for ESFR)? Or is it there because someone can just make money? We can't
>  know unless we religiously follow the RFPs/RFCs and the voting and have
>  photographic memories or wish to spend hours upon hours searching old
>  stuff that's not catalogued or indexed.
>  Perhaps with the state of electronic filing NFPA can make access to the
>  thousands of hours of committee stuff easily accessible. I don't think
>  the intent is to make these deliberations opaque in any way but they
>  are, at this time, translucent at best.
>
>  We have Joe Hankins that can shed light on some of FM reasons and
>  conclusions. Steve addresses 14 intent regularly. Bamford, Dead Bob,
>  Roland (my neighbor that I never see) and others chime in when they know
>  how a committee came to a decision but these guy's memory hardly make an
>  archive.
>
>  Ron Greenman
>  ...at home
>
>
>
>
>
>
>  On Apr 10, 2008, at 4:08 AM, Todd Williams - FPDC wrote:
>
>  > Ron,
>  >
>  > NFPA 13 (2002) sect. 7.2.3.4 states "Check valves shall not be used to
>
>  > subdivide the dry pipe system." To me, that says that check valves
>  > cannot be used for any purpose on a dry system since they will, by
>  > their nature, subdivide a system. Since a check valve is now required
>  > on floor controls, you can probably not install a "floor control" on a
>
>  > dry system. You could install an isolation valve on each floor and
>  > that is about it. (note to thread readers: I did not look up the
>  > specific wording of the 13 section until I prepared this post)
>  >
>  > Todd
>  >
>  >
>  >
>  >> Todd, although you can't use check valves to segregate sections of
>  >> the system you have to have the check valves. Two separate
>  >> requirements.
>  >> One has to do with isolating the floor for service. The other has to
>  >> do with water delivery time.
>  >>
>  >
>  > Todd G. Williams, PE
>  > Fire Protection Design/Consulting
>  > Stonington, Connecticut
>  > www.fpdc.com
>  > 860.535.2080  _______________________________________________
>  > Sprinklerforum mailing list
>  > [email protected]
>  > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>  >
>  > To Unsubscribe, send an email
>  > to:[EMAIL PROTECTED]
>  > (Put the word unsubscribe in the subject field)
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email
>  to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)