Do our hydraulic formulas accurately reflect what really happens in flowing
systems? Yes they have been shown over and over again to be accurate.
In-accurate are the original flow info we base our designs on, as Brian
found out. So do we bucket test the system we know works hydraulically, or
do we verify that the supply is at least as good as entered in the calc's?
(The reason for the annual main drain test, to alert us of systematic
changes to the supply.) For those who can't read Hyd. Calc's to know if they
work, I say start taking classes! If you can't read calc's you probably
can't understand a flow test either, and should certainly not be reviewing
and or approving systems. Bucket Testing is a way for the un-educated to see
in a manner they can understand that the sprinkler system works. It was a
method for AHJ's that had no experience with Hydraulics to review and
approve 13D installations. (One would hope this was in rural areas with
mostly "Volunteer" Departments.) I would hope that as more and more 13D, R
and 13 systems are being installed, that the AHJ's become more "Educated"
and not rely on filling the "Bucket" to prove to themselves that systems
work.
If I sound condescending, I apologize. But this is just another education
opportunity, if we put the right spin on it.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)