Do our hydraulic formulas accurately reflect what really happens in flowing systems? Yes they have been shown over and over again to be accurate. In-accurate are the original flow info we base our designs on, as Brian found out. So do we bucket test the system we know works hydraulically, or do we verify that the supply is at least as good as entered in the calc's? (The reason for the annual main drain test, to alert us of systematic changes to the supply.) For those who can't read Hyd. Calc's to know if they work, I say start taking classes! If you can't read calc's you probably can't understand a flow test either, and should certainly not be reviewing and or approving systems. Bucket Testing is a way for the un-educated to see in a manner they can understand that the sprinkler system works. It was a method for AHJ's that had no experience with Hydraulics to review and approve 13D installations. (One would hope this was in rural areas with mostly "Volunteer" Departments.) I would hope that as more and more 13D, R and 13 systems are being installed, that the AHJ's become more "Educated" and not rely on filling the "Bucket" to prove to themselves that systems work.

If I sound condescending, I apologize. But this is just another education opportunity, if we put the right spin on it.