The reason this issue was addressed is that the prior edition simply
said Buildings With an Unprotected Concealed Space shall have a 3000
sf Remote Area. So if you have a 12 story building with ONE such
space only on the first floor, the 12th floor still had to have a
3000 sf remote area.
It was changed to say adjacent. It doesn't say HORIZONTALLY so it
includes the floor above.
The issue of the office within a warehouse was not discussed (and
guessing where a group of 30 votes will land is often an exercise in
futility) but I would think it is still applicable. Keep in mind
that the area above the office is at a lower density than the rest of
the warehouse (except for the 15 ft overlap)
Roland
On Apr 21, 2008, at 5:16 AM, Russell wrote:
_____
From: Russell [mailto:[EMAIL PROTECTED]
Sent: Friday, April 18, 2008 3:15 PM
To: '[EMAIL PROTECTED]'
Subject: 3000 sq. ft. design area
This subject started from another thread but it brings up some
situations
that exist that have always baffled me. For one, 13 states that the
3000
s.f. is applied to the sprinkler system or portions of the
sprinkler system
adjacent to the unsprinklered concealed area. The floor (and system
on that
floor) above a level that has unsprinklered combustible concealed
spaces is
“adjacent” so why wouldn’t the 3000 s.f. also be required on the level
above? As a matter of fact, as was stated earlier, the fire is
above the
sprinklers on the lower level. Not all buildings have fire rated floor
systems. It is quite common ,as in stick built wood frame condos and
apartments to name a few, to have non rated sub-floors on non rated
floor
framing.
For another, what about a lone 2500 sq. ft. wood framed office/tool
room/restrooms structure with unsprinklered combustible concealed
space,
sorta like an ‘island” in a manufacturing building which is
designed with a
1500 sq. ft. remote are? Should the system at the roof deck above this
“island structure” be designed to 3000 s.f.? Now the roof design is
inadequate unless there was a huge safety margin in its original
design.
Just a thought that’s been bugging me.
Russell Rewis
No virus found in this outgoing message.
Checked by AVG.
Version: 7.5.524 / Virus Database: 269.23.1/1384 - Release Date:
4/17/2008
3:47 PM
No virus found in this outgoing message.
Checked by AVG.
Version: 7.5.524 / Virus Database: 269.23.2/1388 - Release Date:
4/20/2008
3:01 PM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)