Thanks Roland, that helps my feelings.

Russell





-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Monday, April 21, 2008 2:13 PM
To: [email protected]
Subject: Re: 3000 sq. ft. design area

The reason this issue was addressed is that the prior edition simply  
said Buildings With an Unprotected Concealed Space shall have a 3000  
sf Remote Area.  So if you have a 12 story building with ONE such  
space only on the first floor, the 12th floor still had to have a  
3000 sf remote area.

It was changed to say adjacent.  It doesn't say HORIZONTALLY so it  
includes the floor above.

The issue of the office within a warehouse was not discussed (and  
guessing where a group of 30 votes will land is often an exercise in  
futility) but I would think it is still applicable.  Keep in mind  
that the area above the office is at a lower density than the rest of  
the warehouse (except for the 15 ft overlap)

Roland

On Apr 21, 2008, at 5:16 AM, Russell wrote:

>
>
>
>
>    _____
>
> From: Russell [mailto:[EMAIL PROTECTED]
> Sent: Friday, April 18, 2008 3:15 PM
> To: '[EMAIL PROTECTED]'
> Subject: 3000 sq. ft. design area
>
>
>
> This subject started from another thread but it brings up some  
> situations
> that exist that have always baffled me. For one, 13 states that the  
> 3000
> s.f. is applied to the sprinkler system or portions of the  
> sprinkler system
> adjacent to the unsprinklered concealed area. The floor (and system  
> on that
> floor) above a level that has unsprinklered combustible concealed  
> spaces is
> “adjacent” so why wouldn’t the 3000 s.f. also be required on the level
> above? As a matter of fact, as was stated earlier, the fire is  
> above the
> sprinklers on the lower level. Not all buildings have fire rated floor
> systems. It is quite common ,as in stick built wood frame condos and
> apartments to name a few, to have non rated sub-floors on non rated  
> floor
> framing.
>
> For another, what about a lone 2500 sq. ft. wood framed office/tool
> room/restrooms structure with unsprinklered combustible concealed  
> space,
> sorta like an ‘island” in a manufacturing building which is  
> designed with a
> 1500 sq. ft. remote are? Should the system at the roof deck above this
> “island structure” be designed to 3000 s.f.? Now the roof design is
> inadequate unless there was a huge safety margin in its original  
> design.
>
> Just a thought that’s been bugging me.
>
>
>
> Russell Rewis
>
>
>
>
> No virus found in this outgoing message.
> Checked by AVG.
> Version: 7.5.524 / Virus Database: 269.23.1/1384 - Release Date:  
> 4/17/2008
> 3:47 PM
>
>
>
> No virus found in this outgoing message.
> Checked by AVG.
> Version: 7.5.524 / Virus Database: 269.23.2/1388 - Release Date:  
> 4/20/2008
> 3:01 PM
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 269.23.2/1389 - Release Date: 4/21/2008
8:34 AM
 

No virus found in this outgoing message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 269.23.2/1389 - Release Date: 4/21/2008
8:34 AM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to