what is being proposed to you is a line on a riser nipple off of the main
NOT return bends.  The return bend is there for a reason and what is being
proposed to you does not serve the purpose.  The suggestion should be
rejected.

Garth

----- Original Message ----- 
From: "A.P.Silva" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, May 07, 2008 11:08 PM
Subject: Return Bends


> I have a situation, dry system running in heated space below the attic in
> part of the building. In other parts, within the attic space. Where it is
> running in the heated area, sprinklers are pendent type. So the need for
dry
> pendents or return bends. The contractor doesn't want to install
individual
> return bends for each pendent head (for cost reasons). Instead he is
> proposing to make the entire branchline as the return bend. The branchline
> to have a riser at the connection to the main. Then from the branchline
drop
> down directly to each pendent head. Any problems?
>
> Tony
>