That was my understanding also and so having a return bend on the line
would accomplish nothing more in that respect than would occur
normally.

On Thu, May 8, 2008 at 6:51 AM, Mark Sornsin <[EMAIL PROTECTED]> wrote:
> In the case of the dry system, however, they also serve the purpose (I
> believe) to keep water out of the drop.  Once the water enters the drop,
> it's trapped and will eventually corrode the pipe - sometimes to the
> point of sealing the entire diameter.
>
> In the case of a riser nipple on a branch line, the air in the branch
> line will compress enough to allow water into the line, and thus will
> likely enter the drops - for eternity, or until the drop is drained.
>
> Mark A. Sornsin, PE
> Fire Protection Engineer
> Ulteig Engineers, Inc.
> Fargo, ND
> 701.280.8591
> [EMAIL PROTECTED]
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
> Sent: Thursday, May 08, 2008 8:34 AM
> To: [email protected]
> Subject: RE: Return Bends
>
> I know it doesn't seem right. But is it achieving its intent? Return
> bends
> are used to prevent scale and other sediments being trapped at the head.
> To
> some extent, at least except from the individual branchline, won't this
> be
> achieved?
>
> Tony
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Garth W.
> Warren
> Sent: May 8, 2008 5:07 AM
> To: [email protected]
> Subject: Re: Return Bends
>
> what is being proposed to you is a line on a riser nipple off of the
> main
> NOT return bends.  The return bend is there for a reason and what is
> being
> proposed to you does not serve the purpose.  The suggestion should be
> rejected.
>
> Garth
>
> ----- Original Message -----
> From: "A.P.Silva" <[EMAIL PROTECTED]>
> To: <[email protected]>
> Sent: Wednesday, May 07, 2008 11:08 PM
> Subject: Return Bends
>
>
>> I have a situation, dry system running in heated space below the attic
> in
>> part of the building. In other parts, within the attic space. Where it
> is
>> running in the heated area, sprinklers are pendent type. So the need
> for
> dry
>> pendents or return bends. The contractor doesn't want to install
> individual
>> return bends for each pendent head (for cost reasons). Instead he is
>> proposing to make the entire branchline as the return bend. The
> branchline
>> to have a riser at the connection to the main. Then from the
> branchline
> drop
>> down directly to each pendent head. Any problems?
>>
>> Tony
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to